240.4(B) when? #81517
08/24/02 12:10 PM
08/24/02 12:10 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
I am uncertain as to when this section can be sited as a reason for utilizing a breaker with a rating above the ampacity of the conductors being protected. Say, for instance, the ampacity (after all derating) of a set of service conductors is 380A. Since, according to 240.6(A), standard breaker size jumps from 350 to 400A, can the conductors with an ampacity of 380A feed a 400A service?

2017 / 2014 NEC & Related Books and Study Guides
Re: 240.4(B) when? #81518
08/24/02 12:19 PM
08/24/02 12:19 PM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
The 380 amp conductors may be protected by a 400 amp over current device but the maximum calculated load on these conductors can not exceed 380 amps.


Curt Swartz
Re: 240.4(B) when? #81519
08/29/02 10:24 AM
08/29/02 10:24 AM
S
safari  Offline
Member
Joined: Nov 2001
Posts: 11
Newport, Oregon, USA
For service over current protection and conductor coordination you must look in services because the rules are diferent.

230.90.A

This does not allow for selection of the next higher size of over current protection.

tom

Re: 240.4(B) when? #81520
08/29/02 03:32 PM
08/29/02 03:32 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Rounding up to the next standard size is permitted. Take a look at 230.90(A) exception 2 and if you have the handbook, see the commentary following the exception.

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,916
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,510 Are you busy
180,295 Re: Forum
170,799 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.005s) Memory: 0.9577 MB (Peak: 1.0898 MB) Zlib enabled. Server Time: 2018-01-16 11:42:39 UTC