Working clearance #81486
08/22/02 07:35 AM
08/22/02 07:35 AM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
I need some help or suggestions we put a 200amp panel in and right beside it we`ve added a 100 amp generator panel.If I stand in front of the panels straight out I`m clear of all obsticals.But the heating and air guy put the air handler right beside the two panels to the left.I still have 90 degrees for door opening space is this going to work out.I`ve looked over 110.26 and if I`m reading this right my panels would be dead front assemblies and no side clearance needed only front. And here`s another twist he plans on the return over the panels on the outside of the wall but the return will be boxed in. so looking above the panels the wall will go up 3' and protrude out into the room 2'I could turn the panels to 180 and they would be ok for sure but the home owner doesn`t want them there.Thanks for any advice

2017 / 2014 NEC & Related Books and Study Guides
Re: Working clearance #81487
08/22/02 02:27 PM
08/22/02 02:27 PM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
Guess it pays to read the whole artical.I`m moving 2 panels tonight duh the duct work.Well in my defence the a/c guys were not originaly putting the unit here but I`ll have to move the location.One question if they box in the duck work does that change anything.I mean is that the structual ceiling now and I can leave the panels??Or am i splitting hairs here.

Re: Working clearance #81488
08/22/02 02:39 PM
08/22/02 02:39 PM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
A boxed in supply/return duct does not constitute a structural ceiling...this does violate the clear space over panels requirement (if within 6 ft.)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 14 (0.018s) Memory: 0.9493 MB (Peak: 1.0726 MB) Zlib enabled. Server Time: 2018-01-22 18:19:06 UTC