ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Permit Snafus...AHJs and Contractors Jump in
by sparky. 04/28/17 08:11 PM
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,898 Are you busy
169,704 Re: Forum
162,928 Need opinion
Who's Online Now
0 registered members (), 68 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#81486 - 08/22/02 08:35 AM Working clearance  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
I need some help or suggestions we put a 200amp panel in and right beside it we`ve added a 100 amp generator panel.If I stand in front of the panels straight out I`m clear of all obsticals.But the heating and air guy put the air handler right beside the two panels to the left.I still have 90 degrees for door opening space is this going to work out.I`ve looked over 110.26 and if I`m reading this right my panels would be dead front assemblies and no side clearance needed only front. And here`s another twist he plans on the return over the panels on the outside of the wall but the return will be boxed in. so looking above the panels the wall will go up 3' and protrude out into the room 2'I could turn the panels to 180 and they would be ok for sure but the home owner doesn`t want them there.Thanks for any advice


2017 / 2014 NEC & Related Books and Study Guides

#81487 - 08/22/02 03:27 PM Re: Working clearance  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Guess it pays to read the whole artical.I`m moving 2 panels tonight duh the duct work.Well in my defence the a/c guys were not originaly putting the unit here but I`ll have to move the location.One question if they box in the duck work does that change anything.I mean is that the structual ceiling now and I can leave the panels??Or am i splitting hairs here.


#81488 - 08/22/02 03:39 PM Re: Working clearance  
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
A boxed in supply/return duct does not constitute a structural ceiling...this does violate the clear space over panels requirement (if within 6 ft.)



Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7512 MB (Peak: 0.8725 MB) Zlib enabled. Server Time: 2017-04-29 01:41:03 UTC