#81253 - 07/29/02 07:45 PM Main G.E.C used also as an E.G.C  
cthusky  Offline
Junior Member
Joined: Feb 2002
Posts: 6
South Windham Ct, USA
Senerio: Contractor does a 100 amp to 200 amp service upgrade to a single family home. The meter, and 100 amp panel, were located in the basement. The new meter is now located outside of the garage,and a new 200 amp panel is located on the inside wall of the garage. The old panel was left in the basement as a subpanel. The contractor fed the old panel with pvc from the new 200 amp panel. In the pvc are the two ungrounged legs, the neutral,and the main grounding electrode/equipment grounding conductor(one wire which hits a lug on the ground bar{neutral is isolated} then proceeds through the panel to the water meter located a couple feet away).Here's my question. Can the main g.e.c also be used as a e.g.c? I know system grounding is different then equipment grounding, but besides by definition is there an applicible article in the code I can refer to?


2017 / 2014 NEC & Related Books and Study Guides

#81254 - 07/30/02 06:16 AM Re: Main G.E.C used also as an E.G.C  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
cthusky,
if in fact, this is a detatched garage, then both structures would require a GEC, and GE's, and the conductor you mention bettween panels would merely be the EGC.


#81255 - 07/30/02 07:32 PM Re: Main G.E.C used also as an E.G.C  
cthusky  Offline
Junior Member
Joined: Feb 2002
Posts: 6
South Windham Ct, USA
Sparky, no this is an attached garage.


#81256 - 07/31/02 01:08 AM Re: Main G.E.C used also as an E.G.C  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I don't believe anything in the NEC says this can't be done. Just have to make sure you are not setting up parallel neutral paths with incorrect bonding in the sub panel.


#81257 - 08/01/02 05:25 PM Re: Main G.E.C used also as an E.G.C  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
As long as the grounding electrode conductor is continuous and the grounded conductor is not bonded to the grounding conductor, I see no problem with the installation.
Don


Don(resqcapt19)


Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.006s) Memory: 0.7672 MB (Peak: 0.9050 MB) Zlib enabled. Server Time: 2017-10-18 07:11:43 UTC