#81074 - 07/09/02 08:02 PM article 517.13  
qopanel  Offline
Member
Joined: Jul 2002
Posts: 17
Does this article require that you MUST run a grounding conductor with the branch circuits? I failed an inspection today in a patient area of an dentist office, because I did not run a separate grounding conductor to the panel. I used a grounding pig tail from my hospital grade receptacles to the back of my metal 1900 box. All the branch circuits are installed in EMT. Is this type of installation suppossed to be redundant? I really dont have a big problem with having to pull a ground to the receptacles (i've got plenty of room) but, I would like to know for the future if I have made a mistake.

Thanks
Bob


2017 / 2014 NEC & Related Books and Study Guides

#81075 - 07/09/02 08:21 PM Re: article 517.13  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Hi Bob

Yes, you do need to install a separate insulated equipment ground wire. All receptacles and other electrical equipment in patient care areas require redundant grounding (metal raceway with insulated ground wire). Read 517.13(B)

Curt


Curt Swartz

#81076 - 07/09/02 08:41 PM Re: article 517.13  
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
Bob
Where it says shall comply with A and B the B section requires the insulated ground.

517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas.
Wiring in patient care areas shall comply with 517.13(A) and (B).
(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable armor or sheath assembly. The metal raceway system, or cable armor, or sheath assembly, shall itself qualify as an equipment grounding return path in accordance with 250.118. Type AC, Type MC, Type MI cables shall have an outer metal armor or sheath that is identified as an acceptable grounding return path.
(B) Insulated Equipment Grounding Conductor. In an area used for patient care, the grounding terminals of all receptacles and all non–current-carrying conductive surfaces of fixed electric equipment likely to become energized that are subject to personal contact, operating at over 100 volts, shall be grounded by an insulated copper conductor. The grounding conductor shall be sized in accordance with Table 250.122 and installed in metal raceways or metal-clad cables with the branch-circuit conductors supplying these receptacles or fixed equipment.


#81077 - 07/13/02 01:25 PM Re: article 517.13  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Bob,

Watch out if the area is for pediatrics too. You might need tamper resistent receptacles or covers.


#81078 - 07/13/02 02:21 PM Re: article 517.13  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Remember, critical branches can not be installed in AC or MC. (2002 change)

Bob, being that this is a dental facility you probably did not have a critical branch.

In any case your EMT would cover this.

You would still need redundant grounding as the others stated. FYI, you did not need HG receptacles in this installation, unless the equipment itself had HG cord caps.

Roger

[This message has been edited by Roger (edited 07-13-2002).]



Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.042s Queries: 14 (0.028s) Memory: 0.7687 MB (Peak: 0.9058 MB) Zlib enabled. Server Time: 2017-09-22 20:40:05 UTC