#80828 - 05/30/02 04:34 PM continuous loads  
Eandrew  Offline
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
I'm confused over ampacity adjustments.

Table 310-16 is based on a continuous load without exceeding the insulation temp. rating -article 100

so why is the 80% corretion factor for a continuous load needed? Is this lower ampacity not built into table 310-16?

Is it necessary to lower the normal ampacity in 310-16 by 20% and then size the wire and overcurrent protection to 125% of that value. -Erik


2017 / 2014 NEC & Related Books and Study Guides

#80829 - 05/30/02 08:44 PM Re: continuous loads  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Eandrew, article 310-16 is correct. The conductors are rated at 100% and are not the issue in the 80% value. The 80% concerning continuos loads are for OCPD,s and the heat at the connection. If the OCPD is rated for 100% this will not be an issue. I assume by your use of the dash you are refering to the 99 code and if this is the case see 384-16d

Roger


#80830 - 05/31/02 02:36 AM Re: continuous loads  
Eandrew  Offline
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
thanks rodger,

I was thinking that the 80% and 125% related to different things. It is clear to me now. Continuous loads are limited to 80% of the overcurrent device rating. A little algebra and you have an overcurrent device must be at 125% of the continuous load. got it, thanx.


#80831 - 05/31/02 06:16 PM Re: continuous loads  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
You're welcome.

Roger



Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7577 MB (Peak: 0.8881 MB) Zlib enabled. Server Time: 2017-04-24 21:06:36 UTC