ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/21/17 09:27 AM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,222 Are you busy
174,619 Re: Forum
167,046 Need opinion
Who's Online Now
0 registered members (), 56 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#80809 - 05/24/02 03:32 PM grounding 12*12 box  
Eandrew  Offline
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
I had my forman tell me that, for example, if you have a 12*12 box with ten conduits passing straight through, you would not have to terminate each equipment grounding conduit and bond each to the box. He said just one would due. Is this true. I see 250-148a permits one or more. I thought there was a code section which states that all grounds in metal boxes must be spliced together. However, it seems to me to have a terminal strip for ten grounds in a 12*12 is overkill. thank you


2017 / 2014 NEC & Related Books and Study Guides

#80810 - 05/24/02 03:56 PM Re: grounding 12*12 box  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Under the 2002 code, if the EGCs are not spliced or terminated in the box, you don't have to connect any of them to the box. This is assuming that you are using a metallic conduit. In the 1999 code all of the EGCs must be joined together and a connection from the EGCs to the box must be made. You have the correct section, 250-148.
Don(resqcapt19)


Don(resqcapt19)

#80811 - 05/25/02 01:32 PM Re: grounding 12*12 box  
Eandrew  Offline
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
Thank you!

However, I'm still confused.

Code says 250.148 a

"a connection shall be made between the one or more equipment grounding conductors and a metal box by means of a ground screw that shall be used for no other purpose or a listed grounding device"

Now lets say that the job is spec'd out to have equipment grounding conductors in all conduits.

Back to the 12*12 box with 10 equipment grounding conductors inside. According to code one or more must be connected to the box. To me that implies all of them must terminate and be spliced together.

However, 250.148: limits the splicing of equipment grounding conductors only to those associated with circuit conductors that have been spliced. It reads: Where circuit conductors are spliced within a box, or terminated on equipment within a box, any separate equipment grounding conductors associated with those circuit conductors shall be spliced or joined within the box or to the box with devices suitable for the use.

clear as mud?


#80812 - 05/26/02 03:28 PM Re: grounding 12*12 box  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
As Don said,
Unless the conductors are spliced in the box, you needn't terminate your grds.
(this is a new thing in the '02) You might want to check out what version of NEC is applicable.
You didn't mention the voltage. If it's >250 to ground, and that 12x12 came w/ concentrics, you'll have to bond them anyhow.


#80813 - 05/26/02 05:27 PM Re: grounding 12*12 box  
Eandrew  Offline
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
I love this forum. what a life saver. I pretty low down on the totem pole, but i love the fact the I can come here for answers. thank you very much. I can only ask so many stupid questions at work.



Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,138
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7685 MB (Peak: 0.9058 MB) Zlib enabled. Server Time: 2017-07-23 02:42:42 UTC