#80524 - 04/25/02 09:49 PM Relocatable Power Taps  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Just came across this at www.IAEI.org
(I know that some people had asked about it some time ago)
Quote
Relocatable power taps are intended to be directly connected to a permanently installed branch circuit receptacle. Relocatable power taps are not intended to be series connected (daisy chained) to other relocatable power taps or to extension cords. Relocatable power taps are not intended for use at construction sites and similar locations. Relocatable power taps are not intended to be permanently secured to building structures, tables, work benches or similar structures, nor are they intended to be used as a substitute for fixed wiring. The cords of relocatable power taps are not intended to be routed through walls, windows, ceilings, floors or other similar openings

It's in the "UL Corner" (a PDF file)

http://www.iaei.org/pdfs/02_B/02_b_ULQuestionCorner.pdf

Bill


2017 / 2014 NEC & Related Books and Study Guides

#80525 - 04/28/02 05:44 PM Re: Relocatable Power Taps  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
ok....so what are they good for?


#80526 - 05/06/02 10:50 PM Re: Relocatable Power Taps  
CRW  Offline
Member
Joined: Feb 2001
Posts: 159
Bethlehem, PA USA
I just read the IAEI article about this. I can understand why they don't want them to be a substitute for permanent wiring, but I'm confused about the rule not to fasten them to a building structure, work bench, etc. Why then do they have mounting holes?


#80527 - 05/07/02 06:04 AM Re: Relocatable Power Taps  
Trainwire  Offline
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
Huh?
So the one that is fastened to the wall above my workbench so I can plug in my soldering irons, radio(two way), and the charger for my cordless drill, and the one that is daisy chained off of the UPS for the computer are illegal? Do the people that make these rules have any experience in the real world?
Trainwire


#80528 - 05/08/02 12:02 AM Re: Relocatable Power Taps  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Good Questions!

[Linked Image] [Linked Image] [Linked Image]



Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7688 MB (Peak: 0.9046 MB) Zlib enabled. Server Time: 2017-07-22 20:55:56 UTC