#80365 - 04/03/02 11:17 PM service disconnects  
kenrod3020  Offline
Member
Joined: Feb 2002
Posts: 14
ashland ky. us
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?


kenrod3020

2017 / 2014 NEC & Related Books and Study Guides

#80366 - 04/04/02 08:41 AM Re: service disconnects  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]


#80367 - 04/13/02 12:32 PM Re: service disconnects  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?
--
Tom

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison


Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7517 MB (Peak: 0.8771 MB) Zlib enabled. Server Time: 2017-07-22 10:55:33 UTC