ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,854 Are you busy
169,644 Re: Forum
162,889 Need opinion
Who's Online Now
0 registered members (), 49 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#8026 - 03/05/02 04:45 PM Natural Gas thru Copper Pipe  
DB  Offline
Member
Joined: Mar 2002
Posts: 18
St. Louis
This is not an electrical question - exactly. But, it is a trade question.

I was looking at some new housing construction and found they were converting the black iron pipe stubed into the house to copper water pipe using sweated fittings. IS THIS LEAGLE?

I would not want to be the guy to called to fix a gas leak. Could you emagine putting a torch to a gas pipe?


DB

Work Gear for Electricians and the Trades

#8027 - 03/05/02 05:26 PM Re: Natural Gas thru Copper Pipe  
DB  Offline
Member
Joined: Mar 2002
Posts: 18
St. Louis
I mean is the LEGAL?


DB

#8028 - 03/05/02 05:42 PM Re: Natural Gas thru Copper Pipe  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I don't think that you can do this. I know that sometimes copper is used for the final connection to the equipment, but when it is used, it is connected with flare fittings, not sweated joints. I believe that the odor used in the natural gas to make it easier to detect small leaks is corrosive to copper.
A long time ago when I was in high school, I worked part time at the local hardware store. On a very cold winter day a customer came in and bought a 50' length of garden hose and some adapter fitting from hose thread to pipe thread. As he was going out the door, I just had to ask why garden hose in the winter? His reply, "My hose is cold and I'm going to hook up a gas space heater on the other side of the basement".
Don(resqcapt19)


Don(resqcapt19)

#8029 - 03/05/02 06:48 PM Re: Natural Gas thru Copper Pipe  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I am not 100% sure but I beleive that in some parts of the country this is common practice.


#8030 - 03/06/02 03:33 PM Re: Natural Gas thru Copper Pipe  
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
In the UPC the only approved material for gas is: std. weight wrought iron or steel (galvanized or black), yellow brass (containing not more than 75% copper). Approved PE pipe may be used in exterior buried piping systems. (UPC 1210.1) - I believe similar provisions exist in the IPC


#8031 - 03/09/02 06:06 PM Re: Natural Gas thru Copper Pipe  
Phil H  Offline
Member
Joined: Apr 2001
Posts: 21
Tujunga, CA
In the 2000 edition of UPC, 1210.1 changed to allow Types K, L, and ACR copper. The gas must contain less than 0.3 grains of hydrogen sulfide per ft³ (1210.1.1). The joints must be brazed, flared or screwed (1211.2). So the joints can not be sweated with typical plumbing solder and the code requires the brazer to be certified. Also, there are requirements for labeling, supporting and protecting the copper.


#8032 - 03/09/02 09:08 PM Re: Natural Gas thru Copper Pipe  
DB  Offline
Member
Joined: Mar 2002
Posts: 18
St. Louis
Phil,
The pipe joints did look overheated. Maybe they used a siver solder but it did not look brazed.
Thanks for the input.


DB

#8033 - 03/10/02 02:13 PM Re: Natural Gas thru Copper Pipe  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Sorry for the delay, see you actually got an answer. The "International Residential Code" section G2413.5.2 says K and L type coppers are allowed, same restriction for Hydroden Sulfide. G2413.10.2 says joints are made with an approved gas type fitting or brazed, that's where your 'overheated' type joint would come from.

Let's face it guys, were talking about 3 lbs max here, the only real worry is probably piercing the pipe with something.


#8034 - 03/11/02 02:56 PM Re: Natural Gas thru Copper Pipe  
DB  Offline
Member
Joined: Mar 2002
Posts: 18
St. Louis
Thanks for clearing it up. Guess it is legal and safe. It just seems unsafe or least unwise considering the homeowner may decide to try to fix or modify a line himself.

I could also see a ice maker installer tapping the gas line thinking it is a water line.


DB


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,439
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.002s) Memory: 0.7996 MB (Peak: 0.9687 MB) Zlib enabled. Server Time: 2017-04-28 06:28:37 UTC