ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
1913 American Electrician's Handbook
by annemarie1. 07/27/17 03:10 PM
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,368 Are you busy
174,822 Re: Forum
167,214 Need opinion
Who's Online Now
0 registered members (), 63 guests, and 3 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#80186 - 03/14/02 02:09 PM # of Ground rods  
AndrusT  Offline
Member
Joined: Mar 2002
Posts: 22
Whats the rule, on when you need to have 2 ground rods?
I have heard 2 reasons.
1. When the service is over 200 amps.
2. When your water pipe has a plastic main.

I have also heard the reason for this is cause you need 10 feet of ground (rod, or copper main) going into the earth. I can't seem to find this stuff myself. Thanks


2017 / 2014 NEC & Related Books and Study Guides

#80187 - 03/14/02 05:06 PM Re: # of Ground rods  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Unless you've got the $$$ for the tester & time to waste, you'll need 2 rods at all times.

See 250-56 1999 NEC


Few things are harder to put up with than the annoyance of a good example.

#80188 - 03/14/02 05:54 PM Re: # of Ground rods  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
2002 NEC 250.56

A little more explanation:

Unless you have the equipment and time to prove that your one grounding electrode has a resistance of 25 Ohms or less (and the Power Company doesn't mind only one) then the NEC requires no less than two.

Ground Meggers are expensive...

Also, 250.52(A)(5) requires 8 ft to be in contact with the earth. 10 ft. could be your local PoCo requirement.

[This message has been edited by sparky66wv (edited 03-14-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#80189 - 03/14/02 08:34 PM Re: # of Ground rods  
motor-T  Offline
Member
Joined: Nov 2001
Posts: 280
Girard, Ohio, USA
AndrusT:
As it was explained to me by our inspector, he said, " Show me 25 ohms to ground, or drive two ground rods, its that simple."
-Mark-


#80190 - 03/14/02 11:09 PM Re: # of Ground rods  
spkjpr  Offline
Member
Joined: Dec 2000
Posts: 218
Sedalia,MO, USA
Motor t, my inspector is even easier than that. He just says two ground rods no matter what.


#80191 - 03/22/02 06:48 AM Re: # of Ground rods  
joeh20  Offline
Member
Joined: Mar 2002
Posts: 95
Tullahoma, TN, 37388
Our local PoCo went behind their own office and drove 10 8' ground rods and never got 25 ohms. So they let us get by with two now. I worked on a 1200 amp 480v with 5 rods 10' apart cadwelded to 4/0 copper in addition to a clamp on a 4" galvanize water line thirty feet in direct contact with the earth and never got 25 ohms. But the key here was undisturbed earth, seems any fill really messes thing up.


Lighting the way

#80192 - 03/24/02 09:57 PM Re: # of Ground rods  
NonLinearLoad  Offline
Member
Joined: Mar 2002
Posts: 53
McHenry, IL. USA
Illinois.
One rod as supplemental to primary ground as in city supplied water, attachment per code distances, service size to AWG sizing.
Got a well, TWO rods 6' apart all continous wire. Still it gets attached to the first copper accessible to tank as the backup water in the hole deal, got water it gets to the earth.
Wisconsin... TWO rods, due to soil.


#80193 - 04/02/02 07:56 PM Re: # of Ground rods  
electricdiver  Offline
Junior Member
Joined: Apr 2002
Posts: 2
howell,nj,usa
read 250-81 carefully. you don't need any grd rods if you meet the first several conditions


#80194 - 04/02/02 09:25 PM Re: # of Ground rods  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
All you really have to do is have less than 25 ohms to ground on your grounding electrode connection...if it takes 1 rod, or 100.
(rods are kind of a junky ground path. If you're in trouble, you can pour a concrete encased electrode aka:Ufer, by just putting 20' of GEC sized Cu wire in a trench filled with concrete. Unless you have some kind of "resistance dirt", it'll pass)



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.8010 MB (Peak: 0.9671 MB) Zlib enabled. Server Time: 2017-07-28 02:39:53 UTC