Appliance cords #79709
01/13/02 05:04 PM
01/13/02 05:04 PM
E
Electricmanscott  Offline OP
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Can anyone tell me where to find code info on sizing appliance cords? I can not seem to find anything regarding dishwashers in particular. Seems most electrical appliances come with cords rated for less than a 15 or 20 amp circuit. I would like a definitive answer on installing a cord on a dishwasher. Thanks....Scott

2017 / 2014 NEC & Related Books and Study Guides
Re: Appliance cords #79710
01/13/02 10:34 PM
01/13/02 10:34 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Some of the info can be found in 422-16(b)(2). Length 3' to 4' from grounding type plug on cord to rear of appliance.
Then check out 240-4 for wire size and OC protection relative to what the nameplate of your dishwasher says. Probably SP type cord (table 400-4) 14 or 12 AWG. You really need to check out the local code because this is a subject frequently visited and amended by state and local authorities.

Re: Appliance cords #79711
01/14/02 04:57 PM
01/14/02 04:57 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
In general, ampacities of most common types of flexible cord can be found in Table 400-5(A) You can usually use Column B, but check out the small print at the bottom of the table.

Here's an example, 2 burner hot plate draws 20 amps, needs to be on a 30 amp breaker since it will be on all day. Branch circuit conductors are #10, but the cord only needs to be a maximum of #12.


Few things are harder to put up with than the annoyance of a good example.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,573 Are you busy
180,372 Re: Forum
170,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9497 MB (Peak: 1.0738 MB) Zlib enabled. Server Time: 2018-01-21 06:48:12 UTC