Washer in bathroom #79323
12/14/01 09:36 PM
12/14/01 09:36 PM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Is there anything in the NEC to prevent the installation of a washing machine in a bathroom?

I'm assuming that the room is big enough to get a suitable distance from the tub, and I also assume that under the current NEC the recept. would have to be GFI protected.

2017 / 2014 NEC & Related Books and Study Guides
Re: Washer in bathroom #79324
12/14/01 09:55 PM
12/14/01 09:55 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Many apartments have Washer-Dryer combinations in the bathroom. Usually in a nook behind a bi-fold door, though.

Re: Washer in bathroom #79325
12/15/01 04:46 AM
12/15/01 04:46 AM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Thanks. The reason I asked is that it seems to be quite common on the Continent, particularly in Spain, but not here in England.

There's nothing against it here in the IEE Regs., so long as the 6' spacing from the tub can be achieved. It would also have to be hard-wired. I've never seen it done here though.

Re: Washer in bathroom #79326
12/15/01 05:25 AM
12/15/01 05:25 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
Electrically,
here it would be a 'dedicated receptacle' and therefore not GFI. I'm not sure how the spacing, as being next to a basin and/or bath, would affect this.

Practically,
I had one customer, washer in bath, who's agitator was one of those that when up and down, instead of the more common side to side. Given a wet floor, the unit hopped it's way into blocking the door, while yanking it's discharge hose from the standpipe....quite the flood!

Re: Washer in bathroom #79327
12/15/01 10:23 AM
12/15/01 10:23 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
There is no "dedicated receptacle" exception in 210-8(a)(1).
Don(resqcapt19)


Don(resqcapt19)
Re: Washer in bathroom #79328
12/15/01 01:21 PM
12/15/01 01:21 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
hmm, no there isn't, your right.

and we can't just say 210.11(c)(3)EX either , due to 210.11(C)(2) ?!

Looks like a 20A dedicated GFI in a bathrooom ......

Re: Washer in bathroom #79329
12/15/01 03:27 PM
12/15/01 03:27 PM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Sparky,

Kind of a complicated way to go about washing the bathroom floor if you ask me..... [Linked Image]

Why a 20A GFI circuit? With no heating element in U.S. machines, surely a 15A would be sufficient?

Re: Washer in bathroom #79330
12/15/01 05:05 PM
12/15/01 05:05 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,340
Paul,
NEC stipulates a 20A laundry circuit, and if it's in the bath, the 'dedicated' thing we can let fly elsewhere does not here, so GFI it is, and IF it were the sole receptacle on said circuit, it would need to be 20A [Linked Image]

Re: Washer in bathroom #79331
12/15/01 05:56 PM
12/15/01 05:56 PM
P
pauluk  Offline OP
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Fair enough. If it's a 20A circuit with one outlet then a 20A recept. makes sense, and if the NEC says 20A laundry circuit then 20A it is. But I wonder why they specify a cct. that will take up to 2400W for a load that at most will be much less than that, even if you take the 120% rule into account.

Actually, does the NEC consider a washer a continuous load for cct. rating?

Re: Washer in bathroom #79332
12/15/01 06:25 PM
12/15/01 06:25 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,888
NY, USA
Paul,

A Laundry area might also have an Iron being used there that might better justify the 20A circuit.

Bill

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,916
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,510 Are you busy
180,295 Re: Forum
170,799 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.003s) Memory: 1.0229 MB (Peak: 1.1994 MB) Zlib enabled. Server Time: 2018-01-16 11:43:15 UTC