#79293 - 12/11/01 07:03 AM Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
Does an existing fire alarm system that is lacking in current compliance need to be brought up to standards?
I hear this is somewhere in NFPA 72 ( we are still on the '96), but cannot find it.
[Linked Image]


2017 / 2014 NEC & Related Books and Study Guides

#79294 - 12/11/01 07:42 AM Re: Fire Alarm Q  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See NFPA 72, 1999 edition, Section 1-2.3
Unless otherwise noted, it is not intended that the provisions of this document be applied to facilities, equipment, structures, or installations that were existing or approved for construction or installation prior to the effective date of the document.

Exception: Those cases where it is determined by the authority having jurisdiction that the existing situation involves a distinct hazard to life or property.


Joe Tedesco, NEC Consultant

#79295 - 12/11/01 07:00 PM Re: Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
Joe,
Would this apply across the board? I have old pre-ADA systems who's horn/strobes would not comply per today


#79296 - 12/11/01 07:59 PM Re: Fire Alarm Q  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Sparky: I would say yes because this rule is in the first chapter and covers "Fundamentals of Fire Alarm Systems"

The exception would have to be enforced by the AHJ. Did you ask the AHJ about your systems? If they still work I would not consider it as a "distinct hazard."

Just an opinion .....


Joe Tedesco, NEC Consultant

#79297 - 12/12/01 06:05 PM Re: Fire Alarm Q  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
Understood. I think perhaps the confusion is mine, lost bettween code updates and 'change of use' concerning public buildings. I will ask, my AHJ never seems to tire educating me.

[Linked Image]



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7672 MB (Peak: 0.9050 MB) Zlib enabled. Server Time: 2017-04-27 20:42:18 UTC