#79214 - 12/07/01 09:35 AM 7200 V - Feeder or Service?  
Scott Yeazell  Offline
Junior Member
Joined: Dec 2001
Posts: 4
Springfield, OH, USA
A college campus installation starts at a utility owned pole, customer owned 7200V underground conductors run to a customer owned padmounted 7200V switch and fuse, from there 7200V conductors loop to a series of padmount transformers, each feeding a seperate building.
Question: Are the 7200V underground conductors from the switch to the padmount transformers, a feeder or service conductors? Do they require an underground warning ribbon?


2017 / 2014 NEC & Related Books and Study Guides

#79215 - 12/07/01 10:59 AM Re: 7200 V - Feeder or Service?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See the 1999 NEC, Table 300-50, Exception No. 3 for underground installations over 600 volts.

...... A warning ribbon or other effective means suitable for the conditions shall be placed above the underground installation.


Joe Tedesco, NEC Consultant

#79216 - 12/07/01 05:09 PM Re: 7200 V - Feeder or Service?  
Scott Yeazell  Offline
Junior Member
Joined: Dec 2001
Posts: 4
Springfield, OH, USA
Joe,
Table 300-50 Exception No.3 only applies to conduits & raceways that are "under a building or exterior slab" This exception waives the minimum cover requirements. My installation is not under a building or exterior slab, it is direct burial conductors not "conduits or other raceways", and mine are buried according to the minimum cover requirements. Exception #3 doesn't apply in my case.


#79217 - 12/07/01 11:05 PM Re: 7200 V - Feeder or Service?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
You should read this NIOSH report to see if a "warning ribbon" would save a life someday!

http://www.cdc.gov/niosh/pdfs/98-131.pdf


Joe Tedesco, NEC Consultant

#79218 - 12/08/01 07:56 AM Re: 7200 V - Feeder or Service?  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
At a telecoms facility where I worked some years ago, some outside contractors nearly put a JCB digger shovel into a buried 11kV cable.

It was only the hatched black/yellow warning tape that alerted a manager to what was about to happen. The digger crew intended to carry on through the tape (more Darwin Award candidates?) but the boss saw the tape in time to stop them.

Warning tape is cheap. I'd use it.