#78845 - 10/28/01 01:32 PM Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
I was wondering what is the maximum limit of sub-panels that can be installed from a sub-panel that is fed from a main panelboard?

the sub-panel has a main as well as the main panelboard. the first sub-panel is protected on the supply side by a 100A two pole.

the voltage is 120/208.

i want to install a 100 amp sub panel from a 200A sub-panel that is fed from a 200A main panelboard, that also has a 200A main.

i want to use 3 #4 in a 1" emt, using the emt as the egc.

i will place a 100A main in my subpanel.

is this legal? what about 408.16 (A)?

thanks for any replies.

[This message has been edited by frodo (edited 10-28-2001).]


2017 / 2014 NEC & Related Books and Study Guides

#78846 - 10/28/01 01:47 PM Re: Sub-Panels  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
frodo,
If you really need the second 100 amp panel due to load requirements, you might end up shutting down the first 100 amp panel due to overload.
It sounds like a co-ordination issue. Can you feed the second 100 amp panel from the main panel.
Also, do you mean 4 #3s?
And, as has been seen before, using the EMT as EGC is hotly debatable.


#78847 - 10/28/01 01:59 PM Re: Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
there is not much load on the first sub-panel. the main panel is a different story.

i located the subpanel in the building while searching for a route from the main panel.

it would be very difficult to get from the main panel to where the circuit terminates at a 125 subpanel with a 100A main. i decided it would be legal to feed my new subpanel from the 1st subpanel.

as far as the number of conductors i plan to use, i want to use the 1" conduit for the ground, so as to only have to pull in 3 #4's...EMT is permitted as the EGC isnt it?

if not do i have to pull in a foruth conductor?


#78848 - 10/28/01 05:06 PM Re: Sub-Panels  
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
How are you , without violating 310-16, going to protect #4 with 100 A OCP?

[This message has been edited by Glenn (edited 10-28-2001).]


#78849 - 10/28/01 05:30 PM Re: Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
short time overload calculation....

also see 240-3 & 240-3(b)&
110-14(c) and 210-19(a)
"#4 is routinely used for 100A services here" western, ky...i am assuming i can apply the same rule to the #4 with a 100A OCPD? if not i would have to reduce to a 90A OCPD?

the panel is rated 125A

[This message has been edited by frodo (edited 10-28-2001).]

[This message has been edited by frodo (edited 10-28-2001).]

[This message has been edited by frodo (edited 10-28-2001).]


#78850 - 10/28/01 05:39 PM Re: Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
the load is "non-continuos" conductors are 90 degree celcius THHN 120/240 vac

[This message has been edited by frodo (edited 10-28-2001).]


#78851 - 10/28/01 06:06 PM Re: Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
i guess i cant get away with using a 100A OCPD on #4 THHN. the best thing to do would be to reduce the OCPD to 90A at both ends.


#78852 - 10/28/01 06:16 PM Re: Sub-Panels  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Frodo,

The #4 is only allowed for a service to a Dwelling. Anywhere else you have to go according to the tables for ampacity.

Bill


#78853 - 10/28/01 07:31 PM Re: Sub-Panels  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
Frodo,
Read 310.15B6 and table, per Bill's post

Also, the code does not limit how many subpanels are in any given premisis, we could do a 'frankenstien home' with OCPD's in every room ( ok, not the bath..) and as long as 220 was met it would be compliant.


#78854 - 10/28/01 09:48 PM Re: Sub-Panels  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
hi,
thanks for all the input. i appreciate it...i am going to try and find a 90A main to limit the load to 90A...

as always you can count on solid info from ECN

-regards

frodo



Member Spotlight
togol
togol
NW In. USA
Posts: 421