#7858 - 02/26/02 10:16 PM Outlet in Garage for Table Saw  
Phil  Offline
Junior Member
Joined: Feb 2002
Posts: 1
On a 30 amp circuit (10/3 romex and 30 amp breaker), supplying a single outlet in a garage (for a table saw), can a 15 or 20 amp receptacle be used (to match the 15 amp 220 volt plug on the saw), or must it be rated to the full current rating of the circuit, i.e., 30 amp receptacle?

Thanks


Work Gear for Electricians and the Trades

#7859 - 02/26/02 11:25 PM Re: Outlet in Garage for Table Saw  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
Don(resqcapt19)


Don(resqcapt19)

#7860 - 02/27/02 12:09 AM Re: Outlet in Garage for Table Saw  
beach  Offline
Member
Joined: Feb 2002
Posts: 22
You can remove the 30 amp breaker, install a 20 amp, keep the wiring and install a 20 amp receptacle (look for a commercial back wire that will accept 10 awg).

Jon


#7861 - 02/27/02 12:20 PM Re: Outlet in Garage for Table Saw  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
In addition to this, Table 210.21(B)(3) requires a 30 amp receptacle on a 30 amp ckt. regardless of how many receptacles are installed.