#78527 - 10/02/01 04:08 PM sub panel grounding  
ken m  Offline
Member
Joined: Aug 2001
Posts: 58
south carolina
i know this is a particularly worn out question. however, would someone please tell me the code book location that pertains to why a 4 wire feeder is needed for a sub panel that is fed either from the load side of the meter or is fed from a breaker located within the main panel? the local inspectors are looking for backup (reference) when the meter box and the main panel are not located back-to-back and a 4 wire is needed. thx for any help. ken m


2017 / 2014 NEC & Related Books and Study Guides

#78528 - 10/02/01 04:37 PM Re: sub panel grounding  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
250-24(a)(5)
"LOAD SIDE GROUNDING CONNECTIONS. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article."
This is assuming your Main Bonding Jumper is located in the meter enclosure. [Linked Image]


#78529 - 10/02/01 05:02 PM Re: sub panel grounding  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Nick,
It has nothing to do with the location of the main bonding jumper. If there is no service disconnect between the meter and the panel a 4 wire conenction is not required. The grounded conductor can be used to bond anything on the line side of the service disconenct and within the service disconnect enclosure. The 4 wire feeders are only required on the load side of the service disconnecting means.

Don(resqcapt19)


Don(resqcapt19)

#78530 - 10/02/01 05:19 PM Re: sub panel grounding  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Your right! [Linked Image]


#78531 - 10/02/01 07:25 PM Re: sub panel grounding  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See Section 384-20 for the refrence that includes the answer to the question. The NECH also gives a good explanation as to the reason for the isolated neutral in that sub panel.


Joe Tedesco, NEC Consultant


Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.7678 MB (Peak: 0.9054 MB) Zlib enabled. Server Time: 2017-04-25 08:38:11 UTC