#78056 - 08/13/01 07:43 AM Portable cord sizing  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I occasionally wire portable pumps with self-contained 3 ph. starters mounted on the unit. They are fed by plugging into 20 amp branch ckts. A typical size is 1.5 HP (3 amps @ 480 volt). Article 400-13(OC protection for the cords) refers to 240-4. 240-4(a) requires OC protection in accordance with the cords ampacity per table 400-5(A), which requires 12 gauge cord for 20 amps. However, 240-4 allows supplementary OC protection as in 241-10 to protect the cord. Is the OL relay in the starter considered to be this supplementary OC protection, and therefoe, can I use cord smaller than #12, based on OL heater size?


2017 / 2014 NEC & Related Books and Study Guides

#78057 - 08/13/01 07:26 PM Re: Portable cord sizing  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
Redsy;
I'm reading 430-6 The 2nd sentence refers to 400-5, and then ends up in the usual motor tables.
430-22 still applies
of interest,430-42(c) shows a 15 A 99' change


#78058 - 08/13/01 08:13 PM Re: Portable cord sizing  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Sparky,
Thanks. But I'm still hung up on supplementary OC protection as mentioned in 240-4(a). This would allow me to use 14/4 or even 16/4, instead of 12/4 to supply the starter. Remember, it's pulling less than 3 amps, so voltage drop shouldn't be much of a problem. If I can use smaller cable, I'd like to. We usually put about 35' of cord on the pump, and 12/4 can be a nuisance for the operators.


#78059 - 08/13/01 09:15 PM Re: Portable cord sizing  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
ok,
210-4(a) does refer to 400-5.
240-9 would seem to side with you here.
I was looking for some reference in 430, to either code loop there or 'amend' the loop out.
I guess i'm still sittin' the fence here [Linked Image]


#78060 - 08/14/01 07:31 AM Re: Portable cord sizing  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Thanks, sparky.
I like 240-9. It was right in front of my eyes, but I didn't see it.


#78061 - 08/14/01 07:17 PM Re: Portable cord sizing  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
Well i've gone back and forth here, seems you got a winner.
Lemme play devil's advocate... [Linked Image]
Suppose you had a setup with an adjustable setup, like those new Furnace jobs that can 'dial-in' what you need.
Per code that setting can be played with, so would we size to the upper limit of the range???
[Linked Image]


#78062 - 08/14/01 08:40 PM Re: Portable cord sizing  
Anonymous
Unregistered

> would we size to the upper limit of the range???
I should think so unless you can otherwise securely limit the maximum.


#78063 - 08/14/01 10:06 PM Re: Portable cord sizing  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Quote
Originally posted by sparky:
Well i've gone back and forth here, seems you got a winner.
Lemme play devil's advocate... [Linked Image]
Suppose you had a setup with an adjustable setup, like those new Furnace jobs that can 'dial-in' what you need.
Per code that setting can be played with, so would we size to the upper limit of the range???
[Linked Image]


I have 2 of those animals(Smart OL Relay?) on the shelf right now. Allen-Bradley, though. I'm home now, but I recall that even thuogh they are adjustable, you have to choose from a few different ranges for each size starter. This narrows it down somewhat. So, even adjusting all the way up, you won't be going very far for a given relay.



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7907 MB (Peak: 0.9500 MB) Zlib enabled. Server Time: 2017-04-26 00:09:48 UTC