#77257 - 05/17/01 05:12 PM 6x6 gutter  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
can you use a gutter as a raceway? given a six inch by six inch gutter mounted horizontally on the wall is it permissible to install a conduit into one side (bottom) and then exit opposite or at any other location on the top side routing the conductors or cable through the gutter then back into the conduit?

i was told by an electrical supeintendant on the job that this would be a violation...i disagree.

please tell me what you think....


2017 / 2014 NEC & Related Books and Study Guides

#77258 - 05/17/01 05:51 PM Re: 6x6 gutter  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
A wireway is a raceway, see the definition of raceway in Article 100.

Take a look at 362-6 which deals with deflecting conductors in a wireway.

If your installation meets the requirements of 362-6, I don't see any problem.

Tom

[This message has been edited by Tom (edited 05-17-2001).]


Few things are harder to put up with than the annoyance of a good example.

#77259 - 05/17/01 07:29 PM Re: 6x6 gutter  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
Quote
Originally posted by Tom:
A wireway is a raceway, see the definition of raceway in Article 100.

Take a look at 362-6 which deals with deflecting conductors in a wireway.

If your installation meets the requirements of 362-6, I don't see any problem.

Tom

[This message has been edited by Tom (edited 05-17-2001).]


thanks tom,
i thought he was wrong. i spent some time looking up the issue and could not find anything that would restrict a conduit from entering a wireway at a right angle to the wireway and exiting via either directly opposite or from any other location except no less than the distance of six times the largest diameter of the conduit or wireway if installed in the same wall as the conduit that contains the conductor.

please correct me if i am wrong and i appreciate any response

thank you

frodo

[This message has been edited by frodo (edited 05-17-2001).]


#77260 - 05/18/01 07:33 PM Re: 6x6 gutter  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
As far as I can tell, the 6x spacing applies to #4 & larger conductors only and would apply to any two conduits containing that wire, regardless of which wall they enter/leave.

Tom


Few things are harder to put up with than the annoyance of a good example.


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7603 MB (Peak: 0.8920 MB) Zlib enabled. Server Time: 2017-05-23 08:46:33 UTC