#77050 - 04/19/01 04:54 PM Grounding Generators  
cinkerf  Offline
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
Most generators I've seen have an integral circuit breaker. I'll give the following example. A 50KW 120/208V. 3 phase 4/W. The generator would be the only power source to feed a panelboard 50 feet away that will be used in a Park setting for a special event. I would ground and bond at the generator and isolate the neutral in the "remote" panelboard. My feeder assembly would consist of (three) phase conductors, a neutral conductor and an equipment grounding conductor. Does anybody disagree with this installation?

Frank (cinkerf)


2017 / 2014 NEC & Related Books and Study Guides

#77051 - 04/19/01 05:04 PM Re: Grounding Generators  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
So, the generators main would be the main disco, within sight? the panelboard in MLO??

[Linked Image]

[This message has been edited by sparky (edited 04-19-2001).]


#77052 - 04/19/01 05:17 PM Re: Grounding Generators  
cinkerf  Offline
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
Sparky,

I would probably have a main disconnect in the remote panelboard. Grounding is the real point of my question. If the generator has a main circuit breaker then anything downstream of it should be treated as a feeder. At least that is my understanding. I'm just interested in how other people around the country view this and how they ground such an installation.

Frank (cinkerf)


#77053 - 04/19/01 05:47 PM Re: Grounding Generators  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Frank,

Sounds good to me.

[Linked Image]
Bill


#77054 - 04/19/01 05:56 PM Re: Grounding Generators  
Mike  Offline
Member
Joined: Feb 2001
Posts: 62
At the risk of having my opinion rammed down my throat. I will state: you don't need the EGC if you use a non-metallic jacketed multi-conductor cable from the generator to the remote panel and there are no continuous metallic paths (e.g., metal conduit/flex) bonded to the grounding system at the generator and panelboard (no parallel path back to the generator).
You ensure the generator frame is bonded to its grounded conductor. Drive a ground rod near the generator and connect the GEC to the generator's grounded conductor.
Treat the remote panel as a service panel.
Bond the panelboard and EGC buss to the neutral. Drive a ground rod and install a GEC
connected to the neutral in the panelboard.
Or you could do it just the way you described it. Thanks


#77055 - 04/19/01 06:11 PM Re: Grounding Generators  
cinkerf  Offline
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
Mike,

I have seen it done that way. I guess that is why I raised the question in the first place. I wasn't aware that both were acceptable methods. The integral generator circuit breaker is what made me post the question.

Frank (cinkerf)


#77056 - 04/19/01 09:57 PM Re: Grounding Generators  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
Mike;
i'm not going to disagree, as either method could be NEC justified.
But i would like to have some fun with it!

what say we do it that way, and the genny's only 20' away.....real low impedance soil.....somebody must have had a garden or chickenhouse there at one time......

[Linked Image]


#77057 - 04/19/01 10:17 PM Re: Grounding Generators  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Sparky,

Sounds like a good place to open a Bait Stand!

[Linked Image]
Bill


#77058 - 04/20/01 02:18 PM Re: Grounding Generators  
Mike  Offline
Member
Joined: Feb 2001
Posts: 62
Good question, Sparky! Are you suggesting the possibility of a parallel path with the ground rods 20 feet apart? The NEC states that a ground rod must have a 25 ohm or less impedance. A second ground rod is required if the first one is more than 25 ohms. Also, the GEC/rod and grounded conductor are the same potential. And the grounded conductor has the least resistance.


#77059 - 04/20/01 08:25 PM Re: Grounding Generators  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
Mike;
well yes, and apparently code compliant too, jsut fishin' for opinion, beats cuttin' bait!

[Linked Image]



Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.8087 MB (Peak: 0.9823 MB) Zlib enabled. Server Time: 2017-05-28 08:32:35 UTC