#76793 - 03/21/01 09:29 PM URD Cable  
Tim M  Offline
Junior Member
Joined: Mar 2001
Posts: 4
I have spoke to supply houses who use the term URD for a direct burial type of cable similar to triplex. What is this found under in the NEC and UL Whitebook? Is it USE?


2017 / 2014 NEC & Related Books and Study Guides

#76794 - 03/22/01 07:16 AM Re: URD Cable  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
it comes marked USE/URD

[Linked Image]


#76795 - 03/22/01 04:41 PM Re: URD Cable  
Bennie R. Palmer  Offline
Member
Joined: Nov 2000
Posts: 72
Milwaukie, OR 97267 USA
Sparky must be in a hurry [Linked Image] This question appears often, and is asked quite frequently in the field. I have heard of inspectors not allowing cable assemblies identified as URD, for the reasons you state. The inability to locate any approval in publications, is the general reason.
URD, or underground residential distribution cable, can be USE, underground service entrance cable. When it is service entrance cable it is commonly, 3 conductors of Aluminum XHHW, with one conductor identified.
URD identified distribution cable can be medium voltage cable, in the range of 4.16 KV, to 34.5 KV. Of course this will not be marked as USE.


#76796 - 03/22/01 08:27 PM Re: URD Cable  
Tim M  Offline
Junior Member
Joined: Mar 2001
Posts: 4
Thanks. It helps to know what the abbreviations are. I then conclude URD/USE is used for primary and secondary for residential underground, and USE is secondary?


#76797 - 03/22/01 10:30 PM Re: URD Cable  
Bennie R. Palmer  Offline
Member
Joined: Nov 2000
Posts: 72
Milwaukie, OR 97267 USA
Tim: Only URD for 600 volts or less will be identified as USE.
URD for primary medium voltage will be PE, XLP, EPR, PVC, or CSP.



Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7669 MB (Peak: 0.9041 MB) Zlib enabled. Server Time: 2017-04-30 18:45:14 UTC