ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by geoff in UK. 05/29/17 01:05 PM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
237,001 Are you busy
172,018 Re: Forum
164,894 Need opinion
Who's Online Now
0 registered members (), 46 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#75603 - 03/05/07 07:54 PM 320A Meter Pan  
NJ_WVUGrad  Offline
Member
Joined: Jan 2006
Posts: 47
Neptune, NJ, USA
(Sorry - posted this in the wrong area before)

Does anyone know any 320A Meter Pans that are specifically non residential?

I have only found residential models.

It is for an upgrade from a 200A service to a 400A at a Cell Tower Equipment Trailer.

The contract with the client specifies commercial/industrial type equipment only and I am trying to avoid any issues.

I personally would much rather install a CT cabinet, much easier to route conduit & shape 500kcm conductors in. But JCPL is fighting me on using a CT enclosure for a 400A Service.

Thanks for any help.


Work Gear for Electricians and the Trades

#75604 - 03/05/07 10:09 PM Re: 320A Meter Pan  
Fred  Offline
Member
Joined: Apr 2001
Posts: 449
Straughn, IN 47387
What would be the difference between a residential and commercial 320A self contained meterbase?


#75605 - 03/05/07 10:56 PM Re: 320A Meter Pan  
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
I certainly understand that the customer wants to have high-quality components in his electrical system, and in particular wants to avoid the cheapo "contractor specials" often found is residential work. But I don't see the sense in automatically disqualifying something because it's used in residential work. For example, THHN wire is used in residential work in some cases; are you going to not use THHN wire because of that?

It seems to me that he is looking for a particular quality level. Is there perhaps a better way of specifying that that he will be happy with?




[This message has been edited by SolarPowered (edited 03-05-2007).]


#75606 - 03/05/07 11:57 PM Re: 320A Meter Pan  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
well one thing about the class 320 socket here in state of Wisconsin it have two verison either 320 [400 amp ] standard meter or we have 600 amp bolt on metering socket i don't have the website for other POCO for that one but my POCO do have one on the listing.

NJ_WVUGrad you may have to talk to the POCO for the listing of other approved meter socket sometime they do listed it

hope it help here

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#75607 - 03/06/07 08:47 AM Re: 320A Meter Pan  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
To the best of my knowledge, I have not seen a JCP&L (GPU) meter pan rated over 200 amp, with the exception of the 320 for 'resi'.

First Energy (Parent Co.) website may have info you are looking for.

All 'over 200' comm jobs are CT jobs IMHO and experience.

John


John

#75608 - 03/06/07 01:54 PM Re: 320A Meter Pan  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
John, on the commercial we have used the 320, it's rated 320 continous 400 max, if he is running 320 continous IMO it might be a good idea to up the service.
I would not want that cell tower electric bill, with 320 continous.


#75609 - 03/06/07 08:44 PM Re: 320A Meter Pan  
NJ_WVUGrad  Offline
Member
Joined: Jan 2006
Posts: 47
Neptune, NJ, USA
Thanks for the info Hotline

Getting a 400A CT through JCPL engineering is no problem, however getting it by the metering dept is another issue. They seem to be pushing the 320A meter pan for commercial use.

They are also making us a put a disocnnect ahead of the meter for all CT Cabinet jobs - Makes perfect sense to me and have no problem doing it - however they won't get off their a@# and print up a spec showing this.

Makes it hard to justify cost to the client, I get alot of "well contractor XYZ did it last week around the corner with no disco ahead of the meter, why do you say its needed"

Back to topic - the 320Amps is based on running all the radios at full call volume with the DC plant charging and both 5 ton AC's running.

I don't get the privilege (LOL) of performing load calcs - the client does that internally.
I stopped asking questions a long time ago


#75610 - 03/06/07 11:00 PM Re: 320A Meter Pan  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
Les:
That's what this site is all about! As I said, I never used one. You are talking single phase, right?

NJ, the 'Cold Sequence' layout has been around for a while; PSE&G has it also.

Did you check out First Energy web??

John


John

#75611 - 03/07/07 12:05 AM Re: 320A Meter Pan  
homer  Offline
Member
Joined: Sep 2004
Posts: 68
Vancouver, WA, USA
www.b-line.com/product/metering/index.asp might have some information on meter sockets, although you probably have been searching on the Web already. Circle AW seems to have a large selection of meter enclosures.


#75612 - 03/07/07 07:15 AM Re: 320A Meter Pan  
NJ_WVUGrad  Offline
Member
Joined: Jan 2006
Posts: 47
Neptune, NJ, USA
HotLine1

I know it has been around for 480V but I am justing getting into seeing it with 120V

MY main complaint is that by their own admission they have no printed material showing it. And it seems to be only loosely enforced at best - by only a few wiring inspectors


Page 1 of 2 1 2

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.8179 MB (Peak: 0.9910 MB) Zlib enabled. Server Time: 2017-05-30 07:16:02 UTC