Receptacles, radial or daisy chain? #75577
03/05/07 08:12 AM
03/05/07 08:12 AM
I
IanR  Offline OP
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
I have a collegue who is doing a rewire on an old house (1928) The receptacles are all having new runs made to replace the old K&T with 12/2 romex. He wants to run a circuit from the new panel (a beautifully done 200amp center) into a juntion box in the ceiling above the den and then run individual runs out of the box to each outlet (4 total) in a radial fashion. I personally have never seen this, as I am used to the daisy chain method. I was wondering how you all felt about this? While I can't see anything inherently wrong with this, I wonder,is it allowable by the code. I have not seen it directly prohibited, but I may have just missed it. Opinions?

[This message has been edited by IanR (edited 03-05-2007).]

[This message has been edited by IanR (edited 03-05-2007).]

Work Gear for Electricians and the Trades
Re: Receptacles, radial or daisy chain? #75578
03/05/07 08:17 AM
03/05/07 08:17 AM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Nothing wrong with it, as long as that ceiling junction box is accessible after finish (blank cover?).

It may be the case that it is easier to fish wires from the walls into the ceiling space than to drill the studs and fish wire along the walls from box to box.

Re: Receptacles, radial or daisy chain? #75579
03/05/07 08:20 AM
03/05/07 08:20 AM
I
IanR  Offline OP
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
That is what he tells me. The old plaster walls are in good shape and they do not want to cut them up to run the new wires.

[This message has been edited by IanR (edited 03-05-2007).]

Re: Receptacles, radial or daisy chain? #75580
03/05/07 08:21 AM
03/05/07 08:21 AM
I
IanR  Offline OP
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
Thanks for the quick reply.

Re: Receptacles, radial or daisy chain? #75581
03/05/07 08:59 AM
03/05/07 08:59 AM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
That's how the older brick homes are wired wher I live. The home runs are all to the ceiling boxes, from there the receps are fed. Of course there are not a lot of receps.

Re: Receptacles, radial or daisy chain? #75582
03/05/07 09:55 AM
03/05/07 09:55 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
I've used both methods and actually prefer the "radial" that you mention, granted there is adequate access and work space in an accessible attic space where the junction is located. I even put a box above each room or area and then "spider" out from there when appropriate.

You'd be surprised how much easier finish is when you have only one cable coming into each outlet box. I personally find that the time savings in finish make-up out weighs the time it takes to screw in a box and install a few romex connectors.

Re: Receptacles, radial or daisy chain? #75583
03/05/07 11:00 AM
03/05/07 11:00 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Just make sure that box is big enough. You are talking about 11 conductors if I read this right. Add a couple more if this has a switch leg. You also have 5 whites under that big "cludge" nut. Electrically this is fine but mechanically it can be a chore to get this all back in there.


Greg Fretwell
Re: Receptacles, radial or daisy chain? #75584
03/05/07 05:41 PM
03/05/07 05:41 PM
S
steve ancient apprentice  Offline
Member
Joined: Mar 2005
Posts: 169
west springfield,mass
I also prefer this method. As the other person stated just be sure the box is big enough to handle the fill calculation. I find it much easier to run the cables and fish them thru the old plaster walls. I do not do much residential work but as long as the box is assessable (forgive my lousy keyboard skills) and big enough you will find this is a very simple way of doing this. Ive even done it on a new house. Once the boss saw what I did he liked it. Very neat and professional. et us know how this turned out.
Steve

Re: Receptacles, radial or daisy chain? #75585
03/05/07 07:56 PM
03/05/07 07:56 PM
I
IanR  Offline OP
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
Next time I am up that way I will try to take some shots of the finished work and post them here.
Thanks for all of the replies.

[This message has been edited by IanR (edited 03-05-2007).]

Re: Receptacles, radial or daisy chain? #75586
03/05/07 11:03 PM
03/05/07 11:03 PM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
Keep in mind if the attic above could ever be finished these junction boxes will be a problem. I have dealt with this before and it can be a pain to get them outa the way.
Ob


Choose your customers, don't let them choose you.
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,890
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,544 Are you busy
180,351 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.004s) Memory: 1.0237 MB (Peak: 1.1980 MB) Zlib enabled. Server Time: 2018-01-19 07:30:38 UTC