Dazed and confused in Texas #73520
12/26/06 06:44 PM
12/26/06 06:44 PM
W
WFO  Offline OP
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
I work for a POCO where we got a complaint of "partial power". The customers' service comes off of an "underbuilt" service (where the leads from the transformer go from pole to pole and several services tap off of them).
The two services closest to the transformer have good voltage (121 on each leg to ground). At the end of the underbuilt there are four services that all are getting 114 and 126 volts.

"Aha, sez I. Classic neutral problem".

Trouble is, we check and/or redo every connection and still can't correct the problem.

As it turns out, another underbuilt from another transformer terminates on this same pole and it is not having any problems. The neutral for both services is the system neutral and is continuous between both transformers . So we transfer the end services to the other underbuilt and now that one goes from 120/120 to 114/126.

"What the ....???"

So in desperation, the serviceman starts opening the main breakers of each customer and on one, the problem suddenly goes away.
So now, with one guy off, everyone else has good voltage.

My dilemma is what do I tell this guy to fix?
Turning his main off wouldn't impact the neutral.
Any ideas?

P.S. unfortunately, nobody took any amp readings, but they're going back to get some.

Work Gear for Electricians and the Trades
Re: Dazed and confused in Texas #73521
12/26/06 07:55 PM
12/26/06 07:55 PM
L
livetoride  Offline
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
Check the meterbase and ground at his meter. If that is ok turn off all the breakers in the panel; turn them on one at a time till the problem shows up. Then he has a starting point. Good luck Rod

Re: Dazed and confused in Texas #73522
12/26/06 09:44 PM
12/26/06 09:44 PM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 791
Chicago, Il.
That sounds wierd that it would be so precisely offset with varied parallel loading of the source. The only thing that comes to mind is a chance that it could be feeding the primary of a 240/??? transformer with a fault or improper primary tap to neutral. Then you could have two center tap references fighting each other for neighborhood domination. I would expect alot of neutral current there though. I also suppose it would be possible that a damaged surge arrestor could be clamping at a reduced voltage. A scope would reveal a pretty ugly waveform if that were the case.
Joe


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,572 Are you busy
180,371 Re: Forum
170,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.004s) Memory: 0.9502 MB (Peak: 1.0732 MB) Zlib enabled. Server Time: 2018-01-21 06:44:11 UTC