light won't shut off! #7312
01/31/02 12:01 AM
01/31/02 12:01 AM
P
p_riani  Offline OP
Junior Member
Joined: Jan 2002
Posts: 1
Oakland, CA, USA
For 7 years our tenant's hallway light worked by using either of 2 toggle switches. All of a sudden the light won't go off. I've disconnected the wires on both toggle switches and it still doesn't go off!!! The only possible thing that could have changed is the tenant was moving some boxes in the attic where there seems to be some wiring (that doesn't seem to be related). Any thoughts??? Strange, but true!

Work Gear for Electricians and the Trades
Re: light won't shut off! #7313
01/31/02 12:53 AM
01/31/02 12:53 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,888
NY, USA
Hello,

It sounds like wires are making contact somewhere. I had a similar situation where the cause was a screw that had penetrated the cable. You should have it checked out right away.

Bill

Re: light won't shut off! #7314
01/31/02 06:33 AM
01/31/02 06:33 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Check the attic for a shorted cable in the vicinity of the boxes.

Re: light won't shut off! #7315
01/31/02 01:14 PM
01/31/02 01:14 PM
R
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
Reminds me of the story of the serviceman who got a call from an old lady who said that whenever she flushed the toilet the doorbell rang.

Thinking she was a brick short of a load, the serviceman checked it out, only to find the doorbell wiring in the attic was run across some water pipes, and had rubbed a bare spot in the cable. Whenever the toilet was flushed, the pipes vibrated enough to cause the wires to touch together, thus the ding-dong!

Check for a short in the attic.

Rick Miell

Re: light won't shut off! #7316
02/01/02 03:58 AM
02/01/02 03:58 AM
D
dlabrenz  Offline
Member
Joined: Sep 2001
Posts: 25
Muskegon, MI
You didn't say what kind of light this was.
I once had occasion to go on a service call for a similar problem. All of a sudden the light could not be turned off. Turned out to be that the lights were switched on the nuetral instead of the ungrounded conductor,and the ballast in the fixture had the windings go to ground. When the the property owner tryed turning the lights out nothing happened. After changing the ballast the lights worked on the switch again. I also took the time to correct the problem with the switched nuetral.
(Who says nobody calls an electrician when the lights are on ? )

Re: light won't shut off! #7317
02/01/02 05:47 AM
02/01/02 05:47 AM
J
johngeorge  Offline
Member
Joined: Sep 2001
Posts: 26
If the feed for the circuit is in the light fixrure your problem may be in the fixture box itself - conductors cross connected possibly. I would take a look there.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,527 Are you busy
180,327 Re: Forum
170,819 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.005s) Memory: 0.9744 MB (Peak: 1.1203 MB) Zlib enabled. Server Time: 2018-01-17 19:52:38 UTC