#7181 - 01/25/02 09:58 AM 4w ser or 3w seu  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
why can't you use 3w seu with a separate 4awg egc from a service to a subpanel [with an isolated gc]? the egc shouldn't be current carrying so there shouldn't be a problem with impedance or inductive heating... that's why we keep them in the same 4w ser cable, right?


Work Gear for Electricians and the Trades

#7182 - 01/25/02 12:47 PM Re: 4w ser or 3w seu  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
It isn't carrying current under normal conditions. However, in the event of a fault, the fault current may be limited by the reactance of the single conductor, if it is not in close proximity to the conductor feeding the fault. The OCPD might not open in such a case.


#7183 - 01/25/02 08:55 PM Re: 4w ser or 3w seu  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
thank you redsy


#7184 - 01/25/02 10:34 PM Re: 4w ser or 3w seu  
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
Miss Cindy,
If I may ask, where is the subpanel located?


The Watt Doctor
Altura Cogen
Channelview, TX

#7185 - 01/26/02 12:24 AM Re: 4w ser or 3w seu  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
this was in a new house i walked through a few days ago, the meter and 200amp disconnect combo were surface mounted on the side of the garage, and the seu and 4awg cu were run across the garage in the joist bay above, and came down the wall to the 200amp loadcenter, with the isolated gc. it wasn't my job, and i didn't want to stir anything up, so didn't say anything to the contractor.... but i didn't think it was right. if i thought it was real dangerous then i would have said something, thats why i asked here, cause i wouldn't have been able to explain to him why it was a bad idea


#7186 - 01/26/02 10:54 AM Re: 4w ser or 3w seu  
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
This is 300-3(b)(1999) Notice it says 'and all EGCs'. I haven't seen your installation but it sounds like this would cover your situation.


(b) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).


#7187 - 01/26/02 09:28 PM Re: 4w ser or 3w seu  
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Aside from the code issue, it seems like a commonsensical thing to do,'til you get to the point of putting the wiring into the boxes. Doesn't seem likely that they could ever adequately close off the box opening, or adequately clamp the cable, with that extra conductor added to the cable. Of course, I'm sure UL hasn't tested such a set-up, so there's no way to be assured that the connection would work.


#7188 - 01/26/02 10:25 PM Re: 4w ser or 3w seu  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Cindy,

Aside from other considerations, with SEU cable they don't have an insulated grounded (Neutral) conductor.

Bill


#7189 - 01/28/02 12:12 AM Re: 4w ser or 3w seu  
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
Cindy,
Well, I will agree with Steve on this one. The reason that I asked the question above was to get a clear picture of the situation.


The Watt Doctor
Altura Cogen
Channelview, TX


Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7997 MB (Peak: 0.9645 MB) Zlib enabled. Server Time: 2017-07-20 12:36:50 UTC