4w ser or 3w seu #7181
01/25/02 08:58 AM
01/25/02 08:58 AM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
why can't you use 3w seu with a separate 4awg egc from a service to a subpanel [with an isolated gc]? the egc shouldn't be current carrying so there shouldn't be a problem with impedance or inductive heating... that's why we keep them in the same 4w ser cable, right?

Work Gear for Electricians and the Trades
Re: 4w ser or 3w seu #7182
01/25/02 11:47 AM
01/25/02 11:47 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
It isn't carrying current under normal conditions. However, in the event of a fault, the fault current may be limited by the reactance of the single conductor, if it is not in close proximity to the conductor feeding the fault. The OCPD might not open in such a case.

Re: 4w ser or 3w seu #7183
01/25/02 07:55 PM
01/25/02 07:55 PM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
thank you redsy

Re: 4w ser or 3w seu #7184
01/25/02 09:34 PM
01/25/02 09:34 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
Miss Cindy,
If I may ask, where is the subpanel located?


The Watt Doctor
Altura Cogen
Channelview, TX
Re: 4w ser or 3w seu #7185
01/25/02 11:24 PM
01/25/02 11:24 PM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
this was in a new house i walked through a few days ago, the meter and 200amp disconnect combo were surface mounted on the side of the garage, and the seu and 4awg cu were run across the garage in the joist bay above, and came down the wall to the 200amp loadcenter, with the isolated gc. it wasn't my job, and i didn't want to stir anything up, so didn't say anything to the contractor.... but i didn't think it was right. if i thought it was real dangerous then i would have said something, thats why i asked here, cause i wouldn't have been able to explain to him why it was a bad idea

Re: 4w ser or 3w seu #7186
01/26/02 09:54 AM
01/26/02 09:54 AM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
This is 300-3(b)(1999) Notice it says 'and all EGCs'. I haven't seen your installation but it sounds like this would cover your situation.


(b) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).

Re: 4w ser or 3w seu #7187
01/26/02 08:28 PM
01/26/02 08:28 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Aside from the code issue, it seems like a commonsensical thing to do,'til you get to the point of putting the wiring into the boxes. Doesn't seem likely that they could ever adequately close off the box opening, or adequately clamp the cable, with that extra conductor added to the cable. Of course, I'm sure UL hasn't tested such a set-up, so there's no way to be assured that the connection would work.

Re: 4w ser or 3w seu #7188
01/26/02 09:25 PM
01/26/02 09:25 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Cindy,

Aside from other considerations, with SEU cable they don't have an insulated grounded (Neutral) conductor.

Bill

Re: 4w ser or 3w seu #7189
01/27/02 11:12 PM
01/27/02 11:12 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
Cindy,
Well, I will agree with Steve on this one. The reason that I asked the question above was to get a clear picture of the situation.


The Watt Doctor
Altura Cogen
Channelview, TX

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,392 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9992 MB (Peak: 1.1665 MB) Zlib enabled. Server Time: 2018-01-22 16:29:18 UTC