#7032 - 01/20/02 12:08 AM Cap on 3 ph genny w/ rectifier and V reg...  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
OK... all facades aside... It's really the alternator in my truck...

My old alternator's bearings went kaput, so I got a new one from the parts store (the old one was still warranteed)...

The old one had a capacitor mounted on the exterior, the new one didn't, so I took the cap and put it on the new one... They were identical otherwise...

Well, the dern thing will only charge at an idle and doesn't charge very well then... It won't keep the battery charged when the wipers, blower and headlights are on... major voltage drop complete with sputtering motor.

Is it possible that the new alternator has a capacitor that is internal, or otherwise doesn't need the cap that I installed from the old one? Could the "doubled up" caps be causing the problem?

Another note, can't seem to get the belt tight enough for it to stop squeaking too... Might be most of the problem... (glazed?)

I'm going to replace the belt on Monday and see if it helps.

[Linked Image]


[This message has been edited by sparky66wv (edited 01-19-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Work Gear for Electricians and the Trades

#7033 - 01/20/02 01:04 AM Re: Cap on 3 ph genny w/ rectifier and V reg...  
waymag  Offline
Member
Joined: Jan 2002
Posts: 67
dallas, texas, USA
try the new one without the capacitor for a while and see what happens is my only guess.


#7034 - 01/20/02 05:49 AM Re: Cap on 3 ph genny w/ rectifier and V reg...  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Virgil,

The Capacitor used with an Alternator for Autos is probably only there to reduce noise which would interfere with the ECM [Electronic Control Module - the on board Computer], or to get rid of the "Dentists' Drill Whining Sounds" that get impressed into the Audio system's Power Amp.

Question: How bad and at what speed does the drive belt slip / squeal?
Did it begin to squeal on the old Alternator, just prior to it's malfunction?
Have you charged the Battery with an AC to DC charger [a normal Battery charger] and if so, does it hold a charge or does it load the charger constantly [looking for shorted cell(s) in the Battery with this question].

I would verify the conditions of the Battery and make sure there's no equipment that is overloading [ignition coil, radio, etc.], then try getting the belt to not squeak [try running the belt over a bar of soap while the engine is at idle. that should get the belt to stop slipping on the pulley].

The slipping belt is indicating a very high load output [unless the belt/pulley assembly is loose or not fitting correctly]. It's trying to produce as much True Power [Wattage] as is requested, and this is derived from the Horse Power of the Gasoline Motor.

Try charging the Battery with it removed from the car's circuitry [disconnect the posts]. Charge it overnight [at least 6 hours] and see if the charge rate remains high or not.

Shorted cell[s] will make a Battery appear to work OK when lightly loaded [radio on, motor running, etc.]. The underlying problem becomes apparent when trying to start the motor. It either cranks very slowly then quits, or just will not crank at all.

Good luck!

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#7035 - 01/20/02 07:37 AM Re: Cap on 3 ph genny w/ rectifier and V reg...  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
i faintly recall something about 'polarizing' an alternator....


#7036 - 01/20/02 08:27 AM Re: Cap on 3 ph genny w/ rectifier and V reg...  
wolfdog  Offline
Member
Joined: Oct 2001
Posts: 135
Dallas,TX
Polarizing applies to generators. I have to do that with the old Harley generator.


#7037 - 01/20/02 09:47 AM Re: Cap on 3 ph genny w/ rectifier and V reg...  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
You can actually pull the caps on the battery and stick the probes of a meter into the electrolyte, testing from one cell to the next to find a shorted cell. (no volts)
Be sure to clean the probes off when your done of course.


#7038 - 01/20/02 05:44 PM Re: Cap on 3 ph genny w/ rectifier and V reg...  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
New belt...

Problem solved.

Upon closer inspection, I realized that I had the alternator completely against the stop, the belt was stretched beyond the adjustment range and had about an inch of play. (I coulda swore there was only 3/8" of play in it yesterday... hmmmm)

Oh, and thanks for the replies as always...

[This message has been edited by sparky66wv (edited 01-20-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#7039 - 01/20/02 07:51 PM Re: Cap on 3 ph genny w/ rectifier and V reg...  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
ah good! no excuses for monday then....


#7040 - 01/20/02 08:12 PM Re: Cap on 3 ph genny w/ rectifier and V reg...  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Uh... Monday's a holiday...

The supplier is closed (I think)...

Excuses abound!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.002s) Memory: 0.8026 MB (Peak: 0.9692 MB) Zlib enabled. Server Time: 2017-07-25 12:50:13 UTC