#69758 - 09/18/06 12:43 PM R.V. Parks Calculations  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Looking at a R.V. park voltage drops on distances so great. Ideas???. 35 sites two 50 ampers then rest 30-20 amp aprox 100ft to ist then 80 ft between each & two rows.
Makes for some long runs
9600x2=19200 plus 3600 x 33=138000
138000 x 42%(table 551.73)=57960 divided by 240=241.5 amps.
for service calculations .
each row I take it also by 551.73

Pnl ---------------------------------------
----------------------------------------
around 1400 ft each row
additional rows i know would help.
lugs at most good fer 250mcm '
more rows possibly needed
anyone run into this before?

Yoopers


Work Gear for Electricians and the Trades

#69759 - 09/18/06 02:53 PM Re: R.V. Parks Calculations  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Can you move the main distribution to the center of the rows? That way you would have 4 shorter runs instead of 2 long runs.

Larry


#69760 - 09/18/06 03:55 PM Re: R.V. Parks Calculations  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
That is what they try to do in the parks here. They set transformers and maypole out to the lot runs. We found out the allowable calc is probably not going to be enough with these new land yachts.
They tend to use most of the 50a you give then when the AC is on


Greg Fretwell


Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7517 MB (Peak: 0.8733 MB) Zlib enabled. Server Time: 2017-07-23 14:37:07 UTC