#68515 - 08/09/06 07:52 PM romex in underground conduit  
for2aflush  Offline
Junior Member
Joined: Mar 2005
Posts: 5
riverton,nj,us
hello all, I'm trying to win a bet here. My boss said that you can run romex underground in condit . I said you need to run either U.F or thwn. he also said that thhn was fine in the ground as long as it is in conduit. we all know that romex isn't sutable for wet locations, but i cant find in the code that says that underground even in condit is a wet location .. any help would be apprecated . thanks


Work Gear for Electricians and the Trades

#68516 - 08/09/06 09:04 PM Re: romex in underground conduit  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Look in the Definitions under "Location-Wet"

Also, THHN is not fine in the ground if it is in conduit. (I haven't seen any THHN only wire myself, only THHN/THWN)

Now do I get 1/2 the money you win? [Linked Image]


#68517 - 08/09/06 09:21 PM Re: romex in underground conduit  
for2aflush  Offline
Junior Member
Joined: Mar 2005
Posts: 5
riverton,nj,us
i will have to owe it to you ...lol thanks for your responce i looked up wet locations but it never said underground as one


#68518 - 08/09/06 09:50 PM Re: romex in underground conduit  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
From Article 100, Definitions, in the 2005 NEC

Location, Wet. Installations under ground or in concrete slabs or masonry in direct contact with the earth..................

The definition is essentially the same in the 1940 NEC, too [Linked Image]

[This message has been edited by electure (edited 08-09-2006).]



Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7601 MB (Peak: 0.8935 MB) Zlib enabled. Server Time: 2017-04-29 15:42:58 UTC