3-phase no nuetral problem #67720
07/13/06 07:59 PM
07/13/06 07:59 PM
B
bot540  Offline OP
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I have a customer who wants to add a bunch of kitchen equipment into his resteraunt. The problem is that the 120/208 service with a neutral is maxed out. There is another service, 3-phase (120/208) with out a nuetral that is basically un-tapped. The building used to be a machine shop. Is there a solution to this problem that can be fixed with a transformer?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Work Gear for Electricians and the Trades
Re: 3-phase no nuetral problem #67721
07/13/06 08:13 PM
07/13/06 08:13 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
208 implies wye so there should be a neutral at the service disconnect panel although it may have never gone beyond there. This is common in computer rooms too. You should be able to exted that neutral to the load if there is room in the pipe.


Greg Fretwell
Re: 3-phase no nuetral problem #67722
07/13/06 08:32 PM
07/13/06 08:32 PM
B
bot540  Offline OP
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I checked, but not very hard. The switch gear looks like it is from the '50s. I mean it is really old. It's a metal cabinet and when you open it you see 3 metal bus bars with cartridge fuse holders and lugs for the load side. I'm going to get some pics and post on here.


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Re: 3-phase no nuetral problem #67723
07/13/06 09:02 PM
07/13/06 09:02 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Start with the actual service entrance conductors and see if there are 4. It may never get out of the CT can but it really should make it to the MBJ.


Greg Fretwell
Re: 3-phase no nuetral problem #67724
07/13/06 11:50 PM
07/13/06 11:50 PM
M
mahlere  Offline
Member
Joined: Nov 2005
Posts: 507
New Jersey
otherwise, yes, you can create a neutral with a transformer.

Re: 3-phase no nuetral problem #67725
07/14/06 01:00 AM
07/14/06 01:00 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I can't imagine how you can have a wye without a neutral and 208 always means wye doesn't it? That is how it gets grounded. Is there 208 floating delta somewhere?


Greg Fretwell
Re: 3-phase no nuetral problem #67726
07/14/06 04:24 AM
07/14/06 04:24 AM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,409
Vienna, Austria
Quote
I can't imagine how you can have a wye without a neutral and 208 always means wye doesn't it? That is how it gets grounded. Is there 208 floating delta somewhere?

No, not really, but wye only means the transformer has a grounded star point, there is no need to provide a neutral conductor anywhere in the system! For example if you only have symmetrical 3ph loads or all loads are connected in delta (don't forget, a wye system allows you to connect loads both in wye or delta) you won't need a neutral conductor. That's why European motors only have a 3w+ground cord supplying the three phases. Old 3ph plugs didn't even have a neutral terminal. So maybe you need to go all the way up to the transformer.

Re: 3-phase no nuetral problem #67727
07/14/06 08:01 AM
07/14/06 08:01 AM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
250.24 (B) requires the grounded conductor, if there is one, to be brought to the service .
Some installations using 3 phase only try, and sometimes do, omit it but it is needed as a fault path to the transformer.
Check the weather head and see if the drop from the utility co is 4 wire or 3 with a messenger. The messsenger will be bonded at the point of origin.
Alan--


Alan--
If it was easy, anyone could do it.
Re: 3-phase no nuetral problem #67728
07/15/06 08:59 AM
07/15/06 08:59 AM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,409
Vienna, Austria
*smack* I forgot the NEC doesn't allow systems that are grounded via local ground rod only. That rules out a wye system w/o neutral.

Re: 3-phase no nuetral problem #67729
07/15/06 10:58 AM
07/15/06 10:58 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
As I said upthread, computer rooms did not bring the neutral beyond the service disconnect since the standard was only line to line loads. It should still be in the service disconnect enclosure where it gets attached to the main bonding jumper and the grounding electrode. I suppose if you held your nose real tight that connection could be in the metering equipment but I can't see it being very much farther toward the line side.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,548 Are you busy
180,358 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.039s Queries: 15 (0.015s) Memory: 1.0230 MB (Peak: 1.2002 MB) Zlib enabled. Server Time: 2018-01-19 17:41:05 UTC