#67703 - 07/12/06 03:12 PM VFD cable terminations  
jkochan  Offline
Member
Joined: Jan 2005
Posts: 61
Phoenix, AZ USA
We are going to try using Belden 29503 drive cable to solve a EMI/RFI problem we have been posting about for the last couple of months. The runs are about 100' from drives to motors interupted by disconnects at around 80". What effect if any, will sectioning and terminating the cable in the disconnects and continueing on to the motors have on the shielding/dampening properties?


Work Gear for Electricians and the Trades

#67704 - 07/12/06 03:24 PM Re: VFD cable terminations  
Bill39  Offline
Member
Joined: Nov 2001
Posts: 75
Indianapolis, IN, USA
Check with the drive and motor manufacturers.
On some 1336 Rockwell VFD's they had us ground the shield on both ends along with some very specific cable type requirements.