#64290 - 04/04/06 12:30 PM two soda machines  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Was curious to know if (2) soda machines set in the middle of a room could be wired with flexible cord attached to a twist-lock receptacle attached to the ceiling grid of a suspended ceiling. Would 400.7 (A)(6) cover me?


Work Gear for Electricians and the Trades

#64291 - 04/04/06 12:51 PM Re: two soda machines  
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
Also take a look at 422.16(A)

Chris


#64292 - 04/04/06 01:35 PM Re: two soda machines  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
They may want some independent support of the box. Running an extra support wire or two should calm that fear.


Greg Fretwell

#64293 - 04/05/06 01:50 PM Re: two soda machines  
Geno  Offline
Member
Joined: Aug 2001
Posts: 16
Syracuse, NY USA
look at 422.51


#64294 - 04/05/06 05:40 PM Re: two soda machines  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,853
Brick, NJ USA
Shock:
'Cord' cannot be used for permanent wiring methods. That said, IF you have a vend with a cord long enough to reach your receptacle, no problem.

IF you are proposing a twistlock to cord to a 1900 box that the machine cord will plug into; that does not fly.

Dependent on the ceiling height, you may want to consider a power pole, or IMC/RGC from ceiling to floor with the recept(s) installed therein.

John


John

#64295 - 04/05/06 07:18 PM Re: two soda machines  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
By the way vending machines require GFCI protection if integral or by the branch circuit.

2005 - 422.51


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#64296 - 04/05/06 07:56 PM Re: two soda machines  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Hotline1:

Wouldn't a permanently installed cord hanging from a box to a female cord cap be explicitly permitted by 400.7(A)(1)?

-Jon


#64297 - 04/05/06 08:59 PM Re: two soda machines  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
Perhaps I missed what he was trying to do. I was thinking the receptacle was in a box, attached to the grid and it was connected with an article 300 wiring method above the ceiling (MC whip or something).


Greg Fretwell


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,447
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.7920 MB (Peak: 0.9522 MB) Zlib enabled. Server Time: 2017-07-27 16:41:41 UTC