2- 30amp receps #63690
03/23/06 11:46 PM
03/23/06 11:46 PM
D
drgnz23  Offline OP
Member
Joined: Feb 2002
Posts: 56
los angeles
i was just reading another topic from another forum about having 2 30a 220v receptacles on one circuit (welder and compressor) on one 30 amp breaker.(not being used at the same time0).Is this a safe practice? To my knowledge this shouldnt be done regardless if you dont operate at the same time....what do you think?

Work Gear for Electricians and the Trades
Re: 2- 30amp receps #63691
03/24/06 01:08 AM
03/24/06 01:08 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Why not?
I don't know of anything that says you can't have 2 receptacle outlets on a 30a circuit.


Greg Fretwell
Re: 2- 30amp receps #63692
03/24/06 03:12 AM
03/24/06 03:12 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Depends on the load.... 210.21+210.23

And no, over-all I don't think it a safe or wise practice. There is no guarantee of only one in use at a time. One device cycles automaticaly, the other is a welder. [Linked Image] See 630... Although a welder is intermitant, and it is allowed to have multiple welders on the same circuit the OCP and wire size rules are expanded, and differ slightly from a normal branch circuit.

Without knowing the data plates and circuit particulars, I would say, no.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: 2- 30amp receps #63693
03/24/06 03:28 AM
03/24/06 03:28 AM
M
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
Double pole - double throw switch?

Re: 2- 30amp receps #63694
03/24/06 04:35 AM
03/24/06 04:35 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
All of us install multiple receptacle outlets on 15 and 20 amp circuits all the time with no idea at all what will be plugged into them.

Why would this practice suddenly become unsafe once we move to 30 amp circuits?

Article 630 gives us some options for saving money when supplying welders but we do not have to use those options, we can supply a welder with a 30 amp cord cap with a 'standard' 30 amp branch circuit.

I see no NEC reason not to do this, it in my opinion is a design choice.

If the person paying the bill tells me they are fine with one circuit I would have no problem supplying them with one circuit once I explained the circuit may trip if both units operate at the same time.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 2- 30amp receps #63695
03/24/06 07:28 AM
03/24/06 07:28 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
I agree with Bob.
If both units are used at the same time... the circuit breaker will open...exactly what the NEC wants to happen... but the customer, if not warned will not be too happy.


Pierre Belarge
Re: 2- 30amp receps #63696
03/24/06 10:26 AM
03/24/06 10:26 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Assuming the nameplates require similar circuits, I see no problem.

BUT- that's a big assumption. The two appliances are treated quite differently as to wire sizing and over-current protection; Just because they have the same plug is no guarantee. Nevertheless, in Harry Homowners' garage, where Harry is going to putz around solo, it ought to work out OK.
Change that to a guy trying to run a business in his garage....and my answer will change.

Re: 2- 30amp receps #63697
03/24/06 12:38 PM
03/24/06 12:38 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I am fixin' to do exactly the same thing with my welder and a new pressure cleaner I just ordered. In a practical sense I know I could unplug one and plug in the other but I am going to install another receptacle.


Greg Fretwell
Re: 2- 30amp receps #63698
03/24/06 01:50 PM
03/24/06 01:50 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 927
Chicago Illinois USA
I did the same thing at a big honkin' laboratory complex a few years ago. Each lab had a piece of equipment that the staff would roll to different places in the lab based on their particular research project. There were 3 possible locations, but each lab only had 1 machine...1 circuit, 3 receptacles.
Worked great.
No problems...Code or otherwise.


Ghost307
Re: 2- 30amp receps #63699
03/24/06 02:51 PM
03/24/06 02:51 PM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,409
Vienna, Austria
Please tell an innocent European why two appliances with the same voltage and amp draw would need different wire? I assume with some loads you could downsize some for cycling, but generally 30 amps are 30 amps, right?
Trip characteristics are a different piece of cake of course.

I think mainly it's a design thing - we usually put our CEE receptacles on dedicated circuits, so they can be loaded to their full ampacity.

Page 1 of 5 1 2 3 4 5

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,572 Are you busy
180,370 Re: Forum
170,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 1.0278 MB (Peak: 1.2048 MB) Zlib enabled. Server Time: 2018-01-21 04:54:26 UTC