ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2004
Posts: 2
J
Junior Member
I have a G.C. who is on my back about closing a shaft that has to have a mi cable installed. The mi cable is not going to get to the job site for another month. The print shows 3-#2 and a #8gnd M.I. I believe the #8 is a mistake because the copper sheathing will be the equipment ground. Can I sleeve the shaft with EMT or PVC? If I use EMT, do I have to bond the MI cable to the conduit? Is PVC permitted in the shaft? What size conduit should I use and can I have any bends for a 60-foot vertical run?

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
JJ:
Welcome to ECN.
READ Article 332 of '02 NEC (New Jersey)
You can 'fish' MI, and based on a quick read I did not notice any restrictions on putting it in a raceway

WATCH the bend radius, it's based on the OD, & you probably fall in the '9 times'. You need the OD to decide on conduit size. As to PVC, what is the rating of the 'shaft'

John


John
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
I believe the #8 is a mistake because the copper sheathing will be the equipment ground.

Is it possible the 8 AWG is actually a reduced neutral?


Bob Badger
Construction & Maintenance Electrician
Massachusetts