ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by ElectricianBud. 05/27/17 11:02 AM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,938 Are you busy
171,952 Re: Forum
164,832 Need opinion
Who's Online Now
1 registered members (geoff in UK), 47 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#62337 - 02/15/06 02:21 AM 347 lighting  
Cinner  Offline
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Is it proper lockout procedure to shut off the other 2 phases sharing the neutral with thge circuit you are working on?


Work Gear for Electricians and the Trades

#62338 - 02/15/06 08:26 AM Re: 347 lighting  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
yes


Don(resqcapt19)

#62339 - 02/15/06 09:03 AM Re: 347 lighting  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
With power left on two other phases sharing the neutral, if you lifted that neutral at some point you could end up with voltage on one side via the loads.

Not only would this represent a shock-risk to you, it could also unbalance the voltages on those other loads. Given a large load on one phase and a small load on the other, you could see the voltage across the latter rise to almost the phase-to-phase level.


#62340 - 02/15/06 10:16 PM Re: 347 lighting  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You know, this is one thing NEVER mentioned in "lock-out' discussions. The same point also applies to single phase, multi-wire circuits- that is, where two 'legs' share a neutral!

I found this out the hard way...when a money changer was momentarily supplied with 220v...I really loved having to buy a $600 power supply (as part of a $100 add-a-receptacle job)!

An added clarification....if you are "downstream" of any point where the other circuits might be, then there is no need to isolate them as well. But if...as is often the cas...you have all phases present in the run of lights, they all ought to be killed.

[This message has been edited by renosteinke (edited 02-15-2006).]