#6227 - 12/27/01 12:41 AM Wire Torque  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
This question is really aimed at Don (Rescpt19) due to past posts on the subject but anyone with info please chime in!
I am starting a new job that had this requirement in the specifications.
Within 15 days prior to store turn over, re-torque all bolted wire connections in panels and switchboards, in compliance with applicable NEC requirements. Record date, connection location, and torque applied.
We’ll, the NEC doesn’t have any requirements to “re-torque” connections and according to Don it is a very bad practice. What I am wondering is if there is any published data on the consequences of re-torqueing wire connections and the effects it can cause. If I refuse to do this I will need some solid back up. Thanks.


Work Gear for Electricians and the Trades

#6228 - 12/27/01 02:21 AM Re: Wire Torque  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I'm also interested in any ammo to help persuade...

It is common practice for the AHJ's around here to insist upon retorquing when an anti-oxidant has not been used (to apply said "noalox" or "penetrox"). I got a strange look when I asked if he made them cut and re-strip the wire to torque on "virgin" conductor... (sigh)

Lots of DYI work here and the AHJ is usually just happy to see line and load in the right places...

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#6229 - 12/27/01 07:57 AM Re: Wire Torque  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Virgil,
"DYI" referring to "Do Yourself In"? [Linked Image]


#6230 - 12/27/01 10:25 AM Re: Wire Torque  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Nick,
I have been told it is a bad practice, but cannot find any published documents to back up what I think that I was told a number of years ago. Maybe I'm just wrong on this point.
Don(resqcapt19)


Don(resqcapt19)

#6231 - 12/27/01 12:55 PM Re: Wire Torque  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Hee hee... Oooops Typo...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#6232 - 12/27/01 02:49 PM Re: Wire Torque  
WARREN1  Offline
Member
Joined: May 2001
Posts: 176
Greenville, SC, USA
Nick
Ul Standard 486B, Table 1.3 through 1.6. These torque values are used when testing wire connectors, unless the manufacturer assigns another value appropriate for the design. These values are for guidance only if no tightening information is not available on the specific wire connector.
In your case, I think the requirment is written into the specifications so the values will be checked. You don't want to have a loose wire in a connector. Just set your torque wrench to the proper value, then check each one to insure they are all tight. If I were doing the project, I would only hand tighten each connection the first time through, then torque to the proper value on the second time around, noting the values for each one. Your obligation would then be properly fulfilled without overtorque on any connector.
We have this same statement in some of our specs, and I have never given it much thought until I read the thread on this BB. I will re-word my specs to account for this from now on.
Just a thought from the designer.


#6233 - 12/27/01 06:46 PM Re: Wire Torque  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
"Do Yourself In" -- I like it!

As opposed to DIY which really means "Destroy It Yourself."


#6234 - 12/27/01 08:24 PM Re: Wire Torque  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Thanks guys, for the reply's. [Linked Image]


#6235 - 12/27/01 09:26 PM Re: Wire Torque  
motor-T  Offline
Member
Joined: Nov 2001
Posts: 280
Girard, Ohio, USA
I have seen on meter bases especially, a torque spec for different size wire etc. Does anyone really use a torque-wrench ?


#6236 - 12/30/01 04:22 PM Re: Wire Torque  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Yep.

Inspectors up here expect to see one out if they come on site while the meter socket connections are being made.


Al Hildenbrand

Page 1 of 2 1 2

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.8169 MB (Peak: 0.9903 MB) Zlib enabled. Server Time: 2017-04-29 19:34:12 UTC