#62269 - 02/12/06 02:37 PM grounding electrode conductors  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
when derating sevice conductors 4/0 for 3/0 copper for a 200 amp service do you use #2 for the grounding electrode conductor or #4.

[This message has been edited by lite bulb (edited 02-12-2006).]


Work Gear for Electricians and the Trades

#62270 - 02/12/06 07:04 PM Re: grounding electrode conductors  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
There is no relief in 250.66 for derated service conductors. If it is 4/0 copper you need the #2

[This message has been edited by gfretwell (edited 02-12-2006).]


Greg Fretwell


Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7430 MB (Peak: 0.8620 MB) Zlib enabled. Server Time: 2017-04-28 02:38:03 UTC