Feeder Tap #61041
01/15/06 10:05 PM
01/15/06 10:05 PM
M
master66  Offline OP
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
I'm trying to apply one of the tap rules and I just want to make sure I'm doing it correctly.

Here is the situation. Working on the 8th floor of an 8 story office building. There is a 1600 amp 120/208v buss duct running vertically up a chase that is tapped and metered to feed each tennant space as needed.

The drawings show a 400A disconnect being installed to tap the buss duct. The disconnect will be fused at 350 amps.

The problem is, there is no room to install another disconnect and meet all working space clearances.

So, I was thinking that I could install a tap box on the buss and run a feeder to the office space behind the buss where a new closet will be built to house the new electrical equipment.

I will first have to go through a meter then to a fused disconnect. All wiring will be installed in EMT or greenfield.

I know that I won't be able to do this within 10 feet so I am trying to apply the 25' tap rule.

If I am reading 240.21(2)(3) correctly. I can do this if I tap the buss with parallel 300MCM to the disconnect.

Am I correct or can I parallel smaller conductors in this situation.

This is the first time that I ever encountered this situation.

Thanks,
Brian

Work Gear for Electricians and the Trades
Re: Feeder Tap #61042
01/15/06 11:22 PM
01/15/06 11:22 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
240.21B2 requires that the conductor capacity be equal to at least 1/3 of the OC rating. 1600 x 1/3 = 528 amps. 2 #300 at
285 amps = 570 amps. It appears that you have met the requirements of B2 1,2 and3.

Re: Feeder Tap #61043
01/16/06 05:55 AM
01/16/06 05:55 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
I will first have to go through a meter then to a fused disconnect.


That will be a problem.

Quote
240.21(B)(2)(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that will limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,574 Are you busy
180,374 Re: Forum
170,849 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.005s) Memory: 0.9502 MB (Peak: 1.0735 MB) Zlib enabled. Server Time: 2018-01-21 08:35:11 UTC