#5658 - 11/29/01 08:51 PM GFI - spa circuit  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
I previously ran a 50a circuit for a spa and it had no place for a neutral at the spa end, so I did'nt run one. I put in a 50a GFI breaker (not using a neutral) and tested the GFI hot to ground on both legs at the spa and it worked, the GFI did trip fine. Was I wrong for not running a neutral? Even though it trips ok? I'm not sure why this works since GFI's use the nuetral and ground.


The Golden Rule - "The man with the gold makes the rule"

Work Gear for Electricians and the Trades

#5659 - 11/29/01 11:10 PM Re: GFI - spa circuit  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
If the spa did not require a neutral then there are no line to neutral loads. The GFCI breaker is seeing equal balance between the phases and thinks life is rosy. When you connect a phase to ground current flows outside the ground fault circuitry, it sees an imbalance, and trips. No you do not need the neutral. Where would you terminate it?


#5660 - 11/29/01 11:39 PM Re: GFI - spa circuit  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Duh, It just hit me, that makes total sense.
Thanks,


The Golden Rule - "The man with the gold makes the rule"


Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 218
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7492 MB (Peak: 0.8715 MB) Zlib enabled. Server Time: 2017-04-23 21:36:58 UTC