ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,664 Are you busy
169,376 Re: Forum
162,703 Need opinion
Who's Online Now
0 registered members (), 62 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#55315 - 08/25/05 03:16 PM Metal clad , Armored clad ?  
drgnz23  Offline
Member
Joined: Feb 2002
Posts: 56
los angeles
Whats the difference and can you use it in a hospital enviroment in southern california


Work Gear for Electricians and the Trades

#55316 - 08/25/05 06:07 PM Re: Metal clad , Armored clad ?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The difference that counts is the armor jacket of AC cable is a grounding conductor.

The armor of MC cable is generally not a grounding conductor.

If your working in an area that requires redundant grounding you will need to use hospital grade AC cable.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#55317 - 08/25/05 08:08 PM Re: Metal clad , Armored clad ?  
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
iwire,What is hospital grade AC.I'm a canuck so we may not have it here or if we do it's not required.We use just regular ac90.We do use ISO ac90 which has both an insulated ground and bare ground in our LIM panels.


#55318 - 08/25/05 09:18 PM Re: Metal clad , Armored clad ?  
distributor x  Offline
Member
Joined: Jul 2005
Posts: 57
Canada


#55319 - 08/26/05 01:51 PM Re: Metal clad , Armored clad ?  
drgnz23  Offline
Member
Joined: Feb 2002
Posts: 56
los angeles
517.13 (a) All branch circuits serving patient areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having metallic armor or sheath assembly.
Am i reading this wrong


#55320 - 08/26/05 01:59 PM Re: Metal clad , Armored clad ?  
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
drgnz23,

As Bob said, you must use Type HCF cable. This is a form of AC cable, colored green to indicate that it's HCF.

HCF is constructed to include an insulated grounding conductor to meet this requirement. As with all AC cable, the armor is suitable for grounding.


Peter

#55321 - 08/26/05 02:33 PM Re: Metal clad , Armored clad ?  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
drgnz23, you are reading 517.13(A) correctly. The metallic raceway or cable sheath shall itself be a ground path for fault current and there shall also be a wire conductor ground path for fault current.

HCF or HCFC meets this requirement.

Check out this link.
http://www.afcweb.com/table2_.html

Now, depending on what code cycle you are dealing with, you may or may not be allowed to use this wiring method for the "Emergency System" wiring.

Roger

[This message has been edited by Roger (edited 08-26-2005).]


#55322 - 08/26/05 07:37 PM Re: Metal clad , Armored clad ?  
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
I'm curious about how exactly this works--what do you do with the two grounds? I'm guessing that the armor ground is used to ground the box, and the insulated ground is for an isolated ground on the receptacle itself?

I don't understand what the rational is for the two grounds. If someone could explain what advantages they are supposed to bring, I would love to understand this.

Thanks!


#55323 - 08/26/05 08:13 PM Re: Metal clad , Armored clad ?  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
No the 'extra' is not for isolated grounding.

It is simply for redundancy.

Call it a 'back up ground'. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7998 MB (Peak: 0.9670 MB) Zlib enabled. Server Time: 2017-04-25 06:38:17 UTC