#54857 08/09/05 01:45 AM
Joined: Mar 2002
Posts: 125
S
Member
What would be the best possible way to put a sub panel in a detached garage. All wiring will be in 1 1/2" PVC. Ground at gargage. I know no service cable buried in conduit. Should i J-box and change over. It has been along time since I have done one. Thanks.

#54858 08/09/05 02:04 AM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I would just do the PVC stubbed up, wall to wall, LB through the walls and you only end up with 2 90s so pulling is easy. Pull in 4 appropriately sized THHN/THWN and be happy.
With 4 you are not regrounding the neutral at the garage. Drive a rod and ground the garage EGC bus.


Greg Fretwell
#54859 08/09/05 09:30 PM
Joined: Mar 2002
Posts: 125
S
Member
If I run service cable to a j-box and change to THHN that would be acceptable.

#54860 08/09/05 09:46 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
They still may want it sleeved where it comes out of the ground and up the wall. Whether something is subject to "Physical damage" seems to be a local thing.


Greg Fretwell