another pool q #54144
07/18/05 08:23 PM
07/18/05 08:23 PM
F
frank  Offline OP
Member
Joined: May 2001
Posts: 376
windsor ontario canada
A friend had an in ground pool installed with extra low voltage (12v) haywood lights.Gfci protection was installed and does not trip .A rather large shock can be received if you lean over the edge of thr pool and dip you hand into the water. The company that did the install has been working at it for a week now and after trying to blame the fault on the poco now says the problem is that the haywood lights have ground wires that should not be connected. They’er reasoning is that they have been installing this type system for years and the fixtures never had ground wire before. They now have disconnected the grounds and say they are waiting for haywood to send a letter that states it’s ok without ungrounded .This company has called the poco and demanded that they come out and lower the voltage because the lights are rated at 110v and the power to the house is a whopping 125v.Im still lmao and the poco won’t deal with them for obvious reasons .As it stands now the pool can’t be used until this gets figured out. Im not involved and want it to stay that way especially since im sure there was no inspection work industrial exclusively and must say this is not my area of expertise’s. I think that the fault may be under 5 ma and not tripping the breaker( could the ground and neutral be bonded by mistake ?).Any ideas would be appreciated as the installer is asking if I can help because their electricians can’t figure it out. I have told them they had better get it inspected before using it or they will be liable period. thanks

Work Gear for Electricians and the Trades
Re: another pool q #54145
07/19/05 07:52 AM
07/19/05 07:52 AM
M
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
Is everything in, around, and under the pool bonded together, including all electrical devices, per NEC? Galvanic action can set up some pretty good currents. Do you get the problem when the power is off to the lights?
One side of their LV x-fmr (or the center tap) should be tied to ground otherwise you can get a floating voltage that can be very high, especially if there is a problem with the windings in their x-fmr. (Don't change their product, just investigate) Is the x-fmr listed for such a use? I have found many in the past that aren't...


Mike Wescoatt
Re: another pool q #54146
07/19/05 10:54 PM
07/19/05 10:54 PM
F
frank  Offline OP
Member
Joined: May 2001
Posts: 376
windsor ontario canada
Yes the problem only occurss when the lights are energized.I mentioned the xformer center tap to them but don't know if it has been checked.Will also mention the bonding issue as well.thanks again


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,596 Are you busy
180,399 Re: Forum
170,866 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.9501 MB (Peak: 1.0726 MB) Zlib enabled. Server Time: 2018-01-23 04:00:35 UTC