#52662 - 06/01/05 11:32 PM Derating service entrance conductors  
highground  Offline
Member
Joined: Nov 2004
Posts: 53
Chama, NM
When installing a multigang meter socket is there deration allowed for the service entrance conductors? Thanks


Work Gear for Electricians and the Trades

#52663 - 06/02/05 01:00 AM Re: Derating service entrance conductors  
bucketman  Offline
Member
Joined: Oct 2004
Posts: 72
vancouver WA, USA.
I'm trying to think why you would have more than three current carrying conductors in a service enterance.

the only thing I could think of is if it were paralleled.
but still in parallel it's like their the same conductor.


#52664 - 06/02/05 01:24 AM Re: Derating service entrance conductors  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
the biggest issuse is busbar of multi meter socket set up is the rating of main busbar feed to all meters you have to watchout the rating i ran into few of that for incomming service cables and out going cables most meter manufacter will list a warning there


Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#52665 - 06/02/05 08:30 AM Re: Derating service entrance conductors  
highground  Offline
Member
Joined: Nov 2004
Posts: 53
Chama, NM
What I meant was, if you have say a four gang setup with 200+200+200+200 amps do the service entrance conductors need to have an ampacity of 800 amps in a residential setting?
Thanks


#52666 - 06/02/05 09:48 AM Re: Derating service entrance conductors  
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
No, the sum of the metering doesn't neccessarrily need to equal the whole of the service.
See:
Annex D ~ Example D4(a) Multifamily Dwelling; Example D4(b) Optional Calculation for Multifamily Dwelling


The Annex refers back to each applicable article,ie T220.10

A two-family home might require a house panel(40A), an 100A panel(1st floor) and a 60A panel (2nd flr) - but the service might be 150A...depending on the calculated load.


~~ CELTIC ~~
...-= NJ =-...


Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7668 MB (Peak: 0.9032 MB) Zlib enabled. Server Time: 2017-10-23 02:20:52 UTC