#52654 - 06/01/05 11:04 PM Low-V Trasnformer in the main service panel  
JoeMed  Offline
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
Typical doorbell transformer in the panel. I rarely see this but can any one direct me to why or why not, in the NEC 2002, for this type of installation.
Thanks Joe


Work Gear for Electricians and the Trades

#52655 - 06/02/05 12:05 AM Re: Low-V Trasnformer in the main service panel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
Do you mean mounted in a 1/2" KO in the panel? (only the line voltage leads inside) Otherwise how are you separating the class 2 wiring from the line voltage?


Greg Fretwell

#52656 - 06/02/05 12:23 AM Re: Low-V Trasnformer in the main service panel  
JoeMed  Offline
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
thanks for responding, No mounted inside the panel. no separation, all romex install, the low-v wires go out in an opening in the panel, panel is an exterior installation

[This message has been edited by JoeMed (edited 06-02-2005).]


#52657 - 06/02/05 12:43 AM Re: Low-V Trasnformer in the main service panel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
725.55 ?


Greg Fretwell

#52658 - 06/02/05 12:54 AM Re: Low-V Trasnformer in the main service panel  
JoeMed  Offline
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
I'm ckecking it out and re-re reviewind article 450


#52659 - 06/02/05 04:21 PM Re: Low-V Trasnformer in the main service panel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
"JoeMed I'm ckecking it out and re-re reviewind article 450"

Look at 450.1 ex2

450.1 Scope.
This article covers the installation of all transformers.

Exception No. 3: Transformers used with Class 2 and Class 3 circuits that comply with Article 725.


Greg Fretwell

#52660 - 06/02/05 11:04 PM Re: Low-V Trasnformer in the main service panel  
JoeMed  Offline
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
I need clarification on Class 1,2 and 3. Under 725 class 1 not more than 30v.
Can you advise? 725.21 (A)


#52661 - 06/03/05 12:29 AM Re: Low-V Trasnformer in the main service panel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
The short answer is
Class 1, not current limited, treated virtually the same as "power"
Class 2, low voltage, current limited, like your doorbell.
Class 3, higher voltage, still current limited, like a phone line.


Greg Fretwell


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,457
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 14 (0.003s) Memory: 0.7914 MB (Peak: 0.9503 MB) Zlib enabled. Server Time: 2017-09-26 01:43:59 UTC