#52237 - 05/23/05 12:47 PM What would cause this?  
frankft  Offline
Member
Joined: Oct 2004
Posts: 39
Maine
Today I opened up a panel and I saw a 12 awg neutral wire was very melted. I expected to see that a multiwire branch circuit had been miss wired but after tracing the wire back to the nm cable I saw that it was just a single wire circuit. The hot leg of this cable looked fine. I was wondering what would cause this to happen to only 1 conductor out of 20? I'll be going back next week to investigate more, after the homeowner takes down some sheetrock to expose some burried boxes! :-O In the meantime I disconnected the circuit from the breaker and I unconnected the neutral. Any Ideas?


Thats how we do it up in the woods!

Work Gear for Electricians and the Trades

#52238 - 05/23/05 01:07 PM Re: What would cause this?  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Bad connection?? loose screw on neutral bar


#52239 - 05/23/05 01:47 PM Re: What would cause this?  
frankft  Offline
Member
Joined: Oct 2004
Posts: 39
Maine
When I removed the melted wire, the terminal it was under was tight. Thanks for the reply.


Thats how we do it up in the woods!

#52240 - 05/23/05 04:37 PM Re: What would cause this?  
chipmunk  Offline
Member
Joined: Jul 2004
Posts: 144
Southampton, UK
I am thinking (especially with you mentioning buried boxes) that the neutral may possibly have been commoned with other neutrals in one of the boxes, thus acting as the return for other circuits too. It's at least a possibility.


#52241 - 05/23/05 05:11 PM Re: What would cause this?  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I'm with chipmunk on this. Although you see a 2-wire in the panel, it could be carrying 2 or more loads. Especially bad if they are the same phase. Good way to find out is to put an amp-clamp on it, check the load amps, shut the circuit off, and check again. Another is to shut the whole house off, and ring it out through all of the other circuits with the neutral disconnected. In both ways you could still miss it if the load were not on. The sure fire way is to follow it.

Other possibilities could be, and should not be ruled out, is that the breaker is bad, and it fed several space heaters for a while without tripping. The circuit could have a history of abuse, reset and trip cycles, or one big short in the past. Bad connection further in the circuit, or just plain dirty wire. (Dissimular metal, or chemical reaction, or low grade copper, or buss material.)


Mark Heller
"Well - I oughta....." -Jackie Gleason

#52242 - 05/23/05 06:57 PM Re: What would cause this?  
frankft  Offline
Member
Joined: Oct 2004
Posts: 39
Maine
Thanks Chipmunk and e57. I hope I'll see the problem when they open up the ceiling. I told the home owner that since the neutral was melted in the panel, that we could assume that it is melted in other parts of the circuit also. My thoughts are leaning towards finding some neutrals from different circuits tied together. Thanks again.


Thats how we do it up in the woods!

#52243 - 05/23/05 08:59 PM Re: What would cause this?  
John in Jersey  Offline
Junior Member
Joined: Aug 2002
Posts: 7
somerset county, NJ,USA
Funny. No one asked if you ampprobed the noodle. I would have amprobed the hot, then ampprobed the n. This can tell you what is going on..... and also where to start looking


john

#52244 - 05/23/05 09:19 PM Re: What would cause this?  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
John, you really need to post more often. [Linked Image]

I would add that if you would clamp around both the ungrounded and grounded conductor at the same time and the meter reads anything besides zero, we would have a problem if it was suspect of being a two wire circuit.

Roger



Member Spotlight
Admin
Admin
NY, USA
Posts: 3,457
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 14 (0.003s) Memory: 0.7921 MB (Peak: 0.9497 MB) Zlib enabled. Server Time: 2017-09-26 01:52:52 UTC