ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#51559 05/02/05 06:19 AM
Joined: Aug 2001
Posts: 335
S
Member
GFCIs don't work on multiwire circuits because of the shared neutral ... how about AFCIs? Anybody tried? I've learned things the hard way too many times. Figured I'd ask before screwing up.

Joined: Nov 2000
Posts: 2,148
R
Member
Same as GFCIs...you can get expensive 2 pole ones that work on mulitwire circuits.
Don


Don(resqcapt19)
Joined: Feb 2005
Posts: 693
L
Member
Just to cklarify, you can use a multi-wire circuit with GFCI protection as long as you split the neutral where the GFCI's are fed.

That is, by using receptacles, not breakers (unless they're breakers in a sub-panel, in which case, the 'multi-wire circuit' is actually a feeder.)

In other words, the 'load' terminals must have separated neutrals; they can share a single neutral at the 'line' terminals.

I've done this where a jetted bathtub required two GFCI receptacles, for motor(s) and heater. I ran a 12-3 rather than two 12-2's.


Larry Fine
Fine Electric Co.
fineelectricco.com