#51051 - 04/19/05 10:00 PM Abandoned runs  
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I'm doing a rehab job turning a old hotel into a retirement center and there is alot of exsisting openings that will no longer be in use. Does the NEC make mention of abandoned boxes,runs,ect. I wondering if I need to remove these completely to be code complient or if I can just demo the run that feeds these and let them mud over them?


Jesus may have been a capenter,but God was an electrician.Genesis1:3

Work Gear for Electricians and the Trades

#51052 - 04/19/05 10:45 PM Re: Abandoned runs  
highkvoltage  Offline
Member
Joined: Aug 2004
Posts: 34
Massillon, Ohio, USA
I am almost possitive there is a section that you have to remove any unused old conduit, box, equipment and conductors. I remember it from the 2002 NEC code class. I am trying to look it up for you.


#51053 - 04/19/05 11:52 PM Re: Abandoned runs  
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
No, only low voltage. This has been a hot topic for some who would like to see the code changed to require all abandoned wiring and materials removed.

The reason low voltage wiring must be removed is because it adds to the fire/smoke load. Tough to argue that basis when you are talking about pipe and boxes. About the only thing it could be is a workmanship issue which the code does not strictly define.

-Hal


#51054 - 04/20/05 03:06 PM Re: Abandoned runs  
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
On some of the Air Force installations I've been on, any abandoned boxes/conduits were labeled "ABNDN"

I guess one could tag any wires the same way...


Stupid should be painful.

#51055 - 04/20/05 05:43 PM Re: Abandoned runs  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Remember also that this rule for low voltage applies only to the accessible portions of such cables. That does not include cables in raceways, by definition.


Ryan Jackson,
Salt Lake City

#51056 - 04/20/05 09:04 PM Re: Abandoned runs  
highvoltageguy  Offline
Member
Joined: Mar 2005
Posts: 53
Silt, Colorado, USA
anyone know the art.# that says a wire can not be abandoned? I myself when do abandon a wire crimp all the the conductors together (in my area romex)(especially the bare ground)and mark it spare, on both ends. in case some one else down the road decides to hook it back up, with all the conductors tied together should trip a breaker and make who ever do some more investigation. Of course I do agree that removing the abandoned cable is the best choice,and if wires in conduit no problem, but then there's them times!!!!

[This message has been edited by highvoltageguy (edited 04-21-2005).]


#51057 - 04/20/05 10:32 PM Re: Abandoned runs  
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
Oh look ... here's some abandoned cable. It's running from one room to the next inside a conduit. It's been snipped off on each end and is connected to nothing.

Q: is this high voltage? low voltage? or no voltage?


#51058 - 04/21/05 02:02 AM Re: Abandoned runs  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
You never abandon wire. You tape it back on itself and label it "spare".


Greg Fretwell

#51059 - 04/21/05 06:32 AM Re: Abandoned runs  
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
I had this discussion with my local inspector about 6 months back. His (our local county's) interpretation was to either cut the wires off where they enter the boxes or cap them off within the boxes. As long as they were not left bare ended for the next guy to accidently hook up they (AHJ) had no problem. It seemed reasonable and fair to me so we capped them and left them.



Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.8009 MB (Peak: 0.9680 MB) Zlib enabled. Server Time: 2017-10-20 19:55:53 UTC