ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by gfretwell. 09/24/17 12:05 PM
75 kva tranformer
by sparkync. 09/23/17 06:41 PM
Another generator question
by gfretwell. 09/23/17 04:15 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,946 Are you busy
176,740 Re: Forum
168,593 Need opinion
Who's Online Now
0 registered members (), 63 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#50436 - 04/01/05 10:35 PM main lug or breaker for Sub Panel?  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
I am installing a sub panel in an attic space to be finished. It will be fed from a 60A breaker in the main panel in the basement. Would you typically use a main lug panel or main breaker panel for the sub in this situation ?


Work Gear for Electricians and the Trades

#50437 - 04/02/05 12:03 AM Re: main lug or breaker for Sub Panel?  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I almost always use main breaker panels for sub-panels. I consider it an additional disconnect and haven't had any complaints from inspectors yet.

Dave


#50438 - 04/02/05 02:49 PM Re: main lug or breaker for Sub Panel?  
Joey D  Offline
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
Most main breaker panels come with the neutral bar bonded to the ground bar or just have 2 neutral bars bonded together. This would need to be seperate in a sub panel use


#50439 - 04/02/05 04:05 PM Re: main lug or breaker for Sub Panel?  
BobH  Offline
Member
Joined: Oct 2004
Posts: 135
Newfane, N.Y USA
You should be able to do it either way as long as grounded conductor is isolated from grounding conductor and you use a 4 wire feeder.


#50440 - 04/02/05 06:55 PM Re: main lug or breaker for Sub Panel?  
northstar  Offline
Member
Joined: Mar 2005
Posts: 42
Long Island, New York
Im for the Main breaker panel with an Isolated nutreal bar. The added disconnect and protection could only be a good thing. However, the more economical way to go is the main lug which has an iso bar already in it.



Member Spotlight
Admin
Admin
NY, USA
Posts: 3,457
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 14 (0.004s) Memory: 0.7666 MB (Peak: 0.9025 MB) Zlib enabled. Server Time: 2017-09-26 01:49:43 UTC