Double Lug Feeder Wires to Avoid Double Taping the Breaker #50137
03/23/05 10:35 PM
03/23/05 10:35 PM
J
JoeMed  Offline OP
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
This installation has each phase double lugged to avoid double tapping the main service feeder breaker. From the service pedestal there is a 200amp service disconnect that feeds two 100amp panels, each is fed with 2/0 THHN (yes, a tad under) and both the 2/0 are lugged together one slightly longer to accommodate the breaker. To finish the installation, each of the wires go to a separate 100amp main breaker in a 100amp panel. Please advise was this an acceptable solution to this installation? Not my install. I have not seen this before.

Work Gear for Electricians and the Trades
Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker #50138
03/24/05 08:48 AM
03/24/05 08:48 AM
Attic Rat  Offline
Member
Joined: Dec 2003
Posts: 524
Bergen Co.,N.J. USA
...Generally,(2)wires under one lug is a violation,unless that lug/breaker is listed for such..as far as I know,Square D,are the only breakers whose lugs are listed for (2)wires,..but 2/0?? how did they fit (2) of them under(1)lug?? sounds fishy to me...Good Luck!!
Russ

[This message has been edited by Attic Rat (edited 03-24-2005).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker #50139
03/24/05 09:24 AM
03/24/05 09:24 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
I am not aware of any "box" lug (the ones with a hole in them) that is rated for multiple conductors per hole. Lugs with "pressure pads" are often rated for two conductors.

Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker #50140
03/24/05 10:45 AM
03/24/05 10:45 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Any electrical supply house has, or can get, a variety of devices to make this sort of connection properly.
One type has openings for three wires.....use with a short pigtail from the breaker.
The other is a machined block with connections for two wires, and a solid 'tail' that is inserted into the breaker.

Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker #50141
03/24/05 10:53 AM
03/24/05 10:53 AM
J
JoeMed  Offline OP
Member
Joined: Mar 2005
Posts: 16
Chino Valley Az. 86323
thank you for the responses, I was n to clear on the lug. It is a double lug, with one wire in each lug, one wire longer to accommodate the breaker. Sound like it is not as bad as I thought?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9667 MB (Peak: 1.1046 MB) Zlib enabled. Server Time: 2018-01-23 07:57:41 UTC