two wire outlets with no ground #49760
03/15/05 06:31 PM
03/15/05 06:31 PM
N
nov  Offline OP
Member
Joined: Aug 2004
Posts: 69
New Jersey
I need to replace 7 two prong outlets they are feed with two wire BX, but somewhere the BX is feed from knob and tube so no ground. Dont they make a gfci for this situation?

Work Gear for Electricians and the Trades
Re: two wire outlets with no ground #49761
03/15/05 06:55 PM
03/15/05 06:55 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
2002 NEC: "406.3(D) Replacements. Replacement of receptacles shall comply with 406.3(D)(1), (2), and (3) as applicable.
(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or a grounding conductor is installed in accordance with 250.130(C),
grounding-type receptacles shall be used and shall be connected to the grounding conductor in accordance with 406.3(C) or 250.130(C).
(2) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.
(3) Nongrounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (a), (b), or (c).
(a) A nongrounding-type receptacle(s) shall be permitted to be replaced with another nongrounding-type receptacle(s).
(b) A nongrounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuitinterrupter-type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.
(c) A nongrounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s)where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the ground fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding
conductor shall not be connected between the grounding type receptacles."


Earl
Re: two wire outlets with no ground #49762
03/15/05 07:05 PM
03/15/05 07:05 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Also, the armor of old style AC or BX (without the aluminum bonding strip) is not recognized as an equipment grounding means, and in reality on longer runs the armor's resistance is not low enough to trip the breaker if a dead short occurs. If your old house has this kind of AC, then I guess you need to feed the circuit with a GFCI breaker, or find the first receptacle and install a GFCI receptacle there, and wire the rest from "load". Don't forget the stick-on markers.


Earl
Re: two wire outlets with no ground #49763
03/16/05 06:45 AM
03/16/05 06:45 AM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
Short answer:
1) if no ground exists put in a gfci at first recep and feed thru. Leave ground screw empty. You can use 2 or 3 prong receps for the rest of the ckt. Be sure to put stickers on downstream receps. or
2) install new 2 prong receps every place that's ungrounded and forget the gfci


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,392 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.9588 MB (Peak: 1.0911 MB) Zlib enabled. Server Time: 2018-01-22 16:24:25 UTC